The Life Safety Code/101 has an apartment building partial system concept of 
corridors and a sprinkler inside each door opening into the corridors of 
existing buildings.  That concept is in use for one design option for egress.  
Sounds like he is trying to make this apply to an exterior fire escape.  This 
would need some research to see what the CT code actually requires.

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 




--- On Thu, 12/9/10, Todd Williams <[email protected]> wrote:


From: Todd Williams <[email protected]>
Subject: partial egress system
To: [email protected]
Date: Thursday, December 9, 2010, 6:51 AM


I have an AHJ that is requesting a partial system in an existing 8 family 
apartment building (two story). He wants sprinklers by all windows and doors 
near exterior fire escapes and sprinklers under the platforms of the FE's. 
There are no sprinklers currently in the building. When I asked him for the 
Code reference, he said "You're the design professional, you tell me." The CT 
Fire Safety Code is a bastardized version of the IFC and NFPA 101 and I can't 
find any reference to it. Anybody out there heard of such a thing?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to