500 deg heads in a 470 deg oven?  That ain't gonna work.  Do you know the upset 
temperature of the oven?  That is the max potential temperature before the 
over-limit safeties kick in?

Even still 30 degrees is a bit too close for comfort IMHO.  I'd probably 
suggest a small deluge system since you can go with rate compensation type heat 
detection or fixed temp if you desire and make it work.  Otherwise this thing 
could be going off all the time.

Is automatic suppression mandatory for the oven per code?

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Monday, December 13, 2010 3:39 PM
To: [email protected]
Subject: Re: partial egress system

Gotta put 500 degree heads in an Oven that is expected to get as hot as 
470 degrees.... What do I do with the pipe that ties into the overhead 
system...assuming the water will heat up for some distance and then 
possibly affect the 200 degree uprights at the roof.

Help?

Thanks,
Greg
-- 
Greg C. McGahan Living Water Fire Protection, LLC. 1160 McKenzie Road 
Cantonment, FL 32533 850-937-1850 Fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to