Tony,

My take is that you are obligated to provide protection at the deck 1st, and
then everything else becomes a potential obstruction to sprinkler discharge
below.  In this case it seems you will also need to drop protection into the
levels of clouds at the 8' level as well.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of A.P.Silva
Sent: Tuesday, December 14, 2010 10:35 AM
To: [email protected]
Subject: RE: Ceiling "Clouds

I agree with "going in 15' over a suspended ceiling when the space is open
to another area...", but is that in the code?

A different situation. I have a room about 22 ft. high that has some clouds
for acoustics, at about 15 foot level. These are sprinklered up and down.
There are also some clouds 6 feet in diameter at the 8' level, for mounting
light fixtures. So the difference in height from roof to the 6' dia. Clouds
is about 14 feet. Are sprinklers required below these lower clouds? I should
mention, this is a seismic area, and the clouds are supported with wires
from the roof.

Tony

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: December 14, 2010 8:44 AM
To: [email protected]
Subject: RE: Ceiling "Clouds

I don't think so Jimmy.  Up 'til now, the consensus status quo has been to
fully sprinkler up and down but I think a case can be made for going back
15' from the opening in the same spirit as going in 15' over a suspended
ceiling when the space is open to another area ...

SL
 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jimmy Waite
Sent: Tuesday, December 14, 2010 5:52 AM
To: [email protected]
Subject: Ceiling "Clouds

I know this has been talked about before, but I am having trouble getting
onto the archives.  

I have a situation in an auditorium/lecture hall that has a ceiling that
steps down as you get closer to the front of the room.  However, there is
about a 2'-0 perimeter around the room that is open to the non-combustible
space above the ceiling.  In this case I'd be willing to sprinkle around the
opening (sort of like 8.15.1.5 in the '07), but it seems pointless to
provide coverage over this entire lowered ceiling.  Is there any code that
backs this up? I thought I've heard some, but I don't know where it is.


Thanks,

 Jimmy Waite
 Design Engineer

 [email protected]
 mobile: 919.622.7030

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to