Hey, if everybody concerned is happy with the plan, then have at it.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Monday, December 13, 2010 4:38 PM
To: [email protected]
Subject: Re: partial egress system

the 470 is maximum temp the oven is capable of producing under any 
circumstances, the normal operating temp is 350 degrees...

There is no VIABLE alternative to add 4 sprinklers and the Owner / 
Engineer is ok with this arrangement.

Greg

On 12/13/2010 3:36 PM, [email protected] wrote:
> 500 deg heads in a 470 deg oven?  That ain't gonna work.  Do you know the 
> upset temperature of the oven?  That is the max potential temperature before 
> the over-limit safeties kick in?
>
> Even still 30 degrees is a bit too close for comfort IMHO.  I'd probably 
> suggest a small deluge system since you can go with rate compensation type 
> heat detection or fixed temp if you desire and make it work.  Otherwise this 
> thing could be going off all the time.
>
> Is automatic suppression mandatory for the oven per code?
>
> Craig L. Prahl, CET
> Fire Protection
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Greg McGahan
> Sent: Monday, December 13, 2010 3:39 PM
> To: [email protected]
> Subject: Re: partial egress system
>
> Gotta put 500 degree heads in an Oven that is expected to get as hot as
> 470 degrees.... What do I do with the pipe that ties into the overhead
> system...assuming the water will heat up for some distance and then
> possibly affect the 200 degree uprights at the roof.
>
> Help?
>
> Thanks,
> Greg

-- 
Greg C. McGahan Living Water Fire Protection, LLC. 1160 McKenzie Road 
Cantonment, FL 32533 850-937-1850 Fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to