Reviewing a hydraulic calc for a 0.58 over 2000 gridded warehouse system.
All seemed OK until I reached the BOR flow of 1143 gpm.  From this I assume
the selected design area isn't correct since there's no way a 0.58 over 2000
system should flow less than 1160 gpm.  I've never heard of hydraulic
imbalance that results in lower overall flow.  Am I crazy or is there a new
version of sprinkler hydraulics out there?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.