You are not crazy. It could be a rounding error but even at 1160 there have to be no friction loss between flowing nodes.
Ron Fletcher Aero Automatic Phoenix, AZ -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bill Brooks Sent: Thursday, December 16, 2010 2:23 PM To: [email protected] Subject: 0.58 over 2000 Reviewing a hydraulic calc for a 0.58 over 2000 gridded warehouse system. All seemed OK until I reached the BOR flow of 1143 gpm. From this I assume the selected design area isn't correct since there's no way a 0.58 over 2000 system should flow less than 1160 gpm. I've never heard of hydraulic imbalance that results in lower overall flow. Am I crazy or is there a new version of sprinkler hydraulics out there? Bill Brooks William N. Brooks, P.E. Brooks Fire Protection Engineering Inc. _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)
