No sir, Not me.

But an OBVIOUS change of occupancy, I would (and have) tell the owner they
need an engineering evaluation. Otherwise, I am not interested.

R/
Matt

 

 

Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-816-1087 Mobile
318-387-1163 Facsimile
[email protected]

> >-----Original Message-----
> >From: [email protected] [mailto:sprinklerforum-
> >[email protected]] On Behalf Of George Church
> >Sent: Wednesday, January 12, 2011 4:56 PM
> >To: [email protected]
> >Subject: RE: Hydraulic Calcs
> >
> >You're writing up design issues under 25?
> >
> >George Church'
> >Rowe Sprinkler
> >[email protected]
> >570-837-7647
> >
> >-----Original Message-----
> >From: [email protected] [mailto:sprinklerforum-
> >[email protected]] On Behalf Of Matthew J. Willis
> >Sent: Wednesday, January 12, 2011 3:50 PM
> >To: [email protected]
> >Subject: RE: Hydraulic Calcs
> >
> >
> >Yes.
> >I am there to replace parts, with the same parts.
> >
> >Now ask me if I would hang a green tag during a 25 inspection.....
> >
> >R/
> >Matt
> >
> >
> >
> >
> >Matthew J. Willis, CET
> >Automatic Fire Sprinklers
> >Norred Fire Systems L.L.C.
> >318-387-1134 Voice
> >318-816-1087 Mobile
> >318-387-1163 Facsimile
> >[email protected]
> >
> >> >-----Original Message-----
> >> >From: [email protected]
> >> >[mailto:sprinklerforum- [email protected]] On Behalf Of Todd
> >> >Williams
> >> >Sent: Wednesday, January 12, 2011 2:15 PM
> >> >To: [email protected]
> >> >Subject: Re: Hydraulic Calcs
> >> >
> >> >I walked into a 100 year old building with the original system and
> >> >they were storing 10 ft high palletized empty PVC toothpaste tubes.
> >> >The FM had been through the building and had said nothing. If the
> >> >contract was to replace old with new, would you do it?
> >> >
> >> >
> >> >At 02:51 PM 1/12/2011, you wrote:
> >> >>That would be a change of occupancy and so require a new analysis.
> >> >>Different issue. Nothing changes, only replacing the system exactly
> >> >>as it was and it's a repair unless someone like Rich (AHJ) wants to
> >> >>call it otherwise
> >> >>
> >> >>On Wed, Jan 12, 2011 at 11:31 AM, Todd Williams <[email protected]> wrote:
> >> >> > If a system is installed that is an exact duplicate of an
> >> >> > existing
> >> >system,
> >> >> > which it is to replace, is that considered a new system under the
> >> >Code or a
> >> >> > "repair" of a system under 25? Where is the cut-off between the
> >two?
> >> >How
> >> >> > would any of the AHJ's out there address this?
> >> >> >
> >> >> > Now George, supposed your building has 12ft storage of expanded
> >> >plastics or
> >> >> > flammable liquid storage? Most likely the pipe schedule system is
> >> >> > not
> >> >going
> >> >> > to be able to protect those occupancies. Would you swap the
> >> >> > system
> >> >old for
> >> >> > new as it was installed? How would the attorney for the plaintiff
> >> >react to
> >> >> > that?
> >> >> >
> >> >> > I didn't even bring up the issues about 3/4", 3-1/2" and 5" pipe.
> >> >> >
> >> >> >
> >> >> >
> >> >> > At 12:33 PM 1/12/2011, you wrote:
> >> >> >>
> >> >> >> So you run new UG into a building that was legally pipe schedule
> >> >because
> >> >> >> the calc (that wasn't required under the valid but old design
> >> >criteria)
> >> >> >> doesn't work? It doesn't have to, its designed to the applicable
> >> >code at
> >> >> >> installation.
> >> >> >>
> >> >> >> George Church'
> >> >> >> Rowe Sprinkler
> >> >> >> [email protected]
> >> >> >> 570-837-7647
> >> >> >>
> >> >> >> -----Original Message-----
> >> >> >> From: [email protected]
> >> >> >> [mailto:[email protected]] On Behalf Of
> >> >> Todd Williams
> >> >> >> Sent: Wednesday, January 12, 2011 12:20 PM
> >> >> >> To: [email protected]
> >> >> >> Subject: Re: Hydraulic Calcs
> >> >> >>
> >> >> >> Ok, so in Doug's situation, it constitutes a new installation
> >> >> >> and
> >> >not
> >> >> >> repair work (based on your first statement) and it is based on a
> >> >prior
> >> >> >> design. However, as a new installation wouldn't the design need
> >> >> >> to
> >> >meet
> >> >> >> current Codes irregardless of when the design was done and
> >> >> probably require
> >> >> >> hydraulic calculations?
> >> >> >>
> >> >> >
> >> >> > Todd G. Williams, PE
> >> >> > Fire Protection Design/Consulting Stonington, CT
> >> >> > 860.535.2080
> >> >> > www.fpdc.com
> >> >> >
> >> >> > _______________________________________________
> >> >> > Sprinklerforum mailing list
> >> >> > [email protected]
> >> >> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> >> >
> >> >> > For Technical Assistance, send an email to:
> >> >> > [email protected]
> >> >> >
> >> >> > To Unsubscribe, send an email to:Sprinklerforum-
> >> >[email protected]
> >> >> > (Put the word unsubscribe in the subject field)
> >> >> >
> >> >>
> >> >>
> >> >>
> >> >>--
> >> >>Ron Greenman
> >> >>Instructor
> >> >>Fire Protection Engineering Technology Bates Technical College
> >> >>1101 So. Yakima Ave.
> >> >>Tacoma, WA 98405
> >> >>
> >> >>[email protected]
> >> >>
> >> >>http://www.bates.ctc.edu/fireprotection/
> >> >>
> >> >>253.680.7346
> >> >>253.576.9700 (cell)
> >> >>
> >> >>Member:
> >> >>AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC
> >> >>
> >> >>They are happy men whose natures sort with their vocations. -Francis
> >> >>Bacon, essayist, philosopher, and statesman (1561-1626)
> >> >>_______________________________________________
> >> >>Sprinklerforum mailing list
> >> >>[email protected]
> >> >>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> >>
> >> >>For Technical Assistance, send an email to:
> >> >>[email protected]
> >> >>
> >> >>To Unsubscribe, send an email to:Sprinklerforum-
> >> >[email protected]
> >> >>(Put the word unsubscribe in the subject field)
> >> >
> >> >Todd G. Williams, PE
> >> >Fire Protection Design/Consulting
> >> >Stonington, CT
> >> >860.535.2080
> >> >www.fpdc.com
> >> >
> >> >_______________________________________________
> >> >Sprinklerforum mailing list
> >> >[email protected]
> >> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> >
> >> >For Technical Assistance, send an email to: [email protected]
> >> >
> >> >To Unsubscribe, send an email
> >> >to:[email protected]
> >> >(Put the word unsubscribe in the subject field) No virus found in
> >> >this incoming message.
> >> >Checked by AVG - www.avg.com
> >> >Version: 9.0.872 / Virus Database: 271.1.1/3374 - Release Date:
> >> >01/12/11
> >> >01:38:00
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >No virus found in this incoming message.
> >Checked by AVG - www.avg.com
> >Version: 9.0.872 / Virus Database: 271.1.1/3375 - Release Date: 01/12/11
> >01:38:00

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to