With the Multi floor jobs we've done, it became practical after doing a calc
for the top floor (7th), to do a new calc for the 4th to minimize the pipe
sizes. At that point no further pipe size advantage could be gained, since
1st floor was all merchantile, and B1 and B2 were dis-simular parking
levels.

At some level it makes economic sense to re-calc, and the poorer your supply
the earlier you'll see that impact. Every floor?? If the supply just barely
makes the top floor, the elevation gain alone may make a new calc cost
effective. This is generally the case where Manual standpipes are allowed.
(Less than 75') once the standpipe is pump fed, there need to be several
floors before size change can make significant cost impacts (savings).

Thom
This has been our experience, your experience may differ.


What's the view of the Forum on whether a floor is a system?

Roland