The question is not can you configure it like a system riser and call it at YOUR choice a system. The question is MUST it be a system? As for the components one elects to put on each floor, NFPA 13 does not require all the stuff shown in A.8.17.4.2(b) for a floor control valve (actually the criteria in 13 that the annex material is attached to is not about floor control valves). Other sections indicate the type of supervision for floor control valves but nothing in 13 says you have to have it. Now the IBC requires a control valve but then it is real sloppy on the alarm requirements (many things interpreted to mean a flow switch per floor but nada explicitly stating on it). A tad amusing.

There are significant impacts on whether each floor is a system especially for NFPA 25.

Roland


On Jan 13, 2011, at 10:39 AM, Todd Williams wrote:

If the floor has its own dedicated feed from the system riser, then yes it can be a system. If it has a common feed with other floors, then it isn't. See NFPA 13 section 3.3.21 (assuming we accept that the word "system" here means sprinkler system).