The commentary to IBC 2009 clarifies this issue.

An excerpt is as follows:

"The text's specific wording that the secondary supply be "on-site" would
preclude the use, for example, of a second connection to the municipal water
supply remote from the primary connection to achieve compliance with this
requirement."





Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Shelton, Eric
Sent: Tuesday, February 15, 2011 3:54 PM
To: [email protected]
Cc: Howell Taylor
Subject: IBC 2006, section 903.3.5.2

Posting this for a friend having technical difficulties ......

 

 

IBC section 903.3.5.2 is about the provision of secondary water supply
for high-rise buildings in certain seismic zones.  My question is, does
the definition of secondary water supply include separate underground
piping to feed the building or can the secondary water supply tie into
the primary underground piping prior to entering the building or
anywhere else on site.

 

Eric J. Shelton, PE

Senior Fire Protection Engineer

AECOM Design

Direct 540.857.3282

AECOM

10 South Jefferson Street, Suite 1600

Roanoke, Virginia 24011
T 540.857.3100   F 540.857.3180

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to