To all; Take a look at NFPA 14 Figure A.7.1 (c) for a typical multi zone system with gravity tanks supplying the lower zone pump or acting as a suction source, should comply with the requirements of IBC 2006, Section 903.3.5.2. Be careful when designing the system to make sure pressure and flows balance and gravity tanks pressures on the sprinkler system supply connection balance with the pressure and flows of the fire pump for that zone.
Regards Jim Jim Davidson Davidson Associates Fire Protection * Medical Gas * Code Consulting 302-994-9500 Fax:302-234-1781 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of steve Sent: Wednesday, February 16, 2011 1:01 PM To: AFSA Subject: Re: IBC 2006, section 903.3.5.2 As Thom says, we do it all the time. I've never done a high-rise any other way. We cast a break tank of 20,000 gallons monolithically with the lowest level of structure on grade (usually the parking basement). The best spot is often the bulkhead at the bottom of the ramp. The tank is filled by three inlets, two automatic and one manual. The new building code requires two service laterals into the building - everything is redundant now except the pump, ironically. SML Sent from my Verizon Wireless BlackBerry -----Original Message----- From: "Thom" <[email protected]> Sender: [email protected] Date: Wed, 16 Feb 2011 10:41:57 To: <[email protected]> Reply-To: [email protected] Subject: RE: IBC 2006, section 903.3.5.2 Bill: I think if you check back about a year or 2 ago we were talking about this same thing, and Steve Leyton said "It is common for us to have a on-site storage for the secondary water supply." At the time I believe he used the example of a Concrete enclosure under the Parking entry ramp of garage level of a high rise as the stored water source on site, which supplied the fire pump. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bill Brooks Sent: Wednesday, February 16, 2011 8:08 AM To: [email protected] Subject: RE: IBC 2006, section 903.3.5.2 What kind of high-rise building are you thinking about where there is space available for two sets of tanks and pump houses? I've never seen a high-rise sprinkler system fed from a site pump and tank. I suppose a pump and tank buried in plaza would be OK as the secondary but you would have to engineer the entire secondary system to withstand the seismic event. I've always assumed this secondary supply is located inside the building. Bill Brooks William N. Brooks, P.E. Brooks Fire Protection Engineering Inc. 372 Wilett Drive Severna Park, MD 21146-1904 410-544-3620 410-544-3032 FAX 412-400-6528 Cell _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)