Bill:

I think if you check back about a year or 2 ago we were talking about this
same thing, and Steve Leyton said "It is common for us to have a on-site
storage for the secondary water supply." At the time I believe he used the
example of a Concrete enclosure under the Parking entry ramp of garage level
of a high rise as the stored water source on site, which supplied the fire
pump.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bill Brooks
Sent: Wednesday, February 16, 2011 8:08 AM
To: [email protected]
Subject: RE: IBC 2006, section 903.3.5.2

What kind of high-rise building are you thinking about where there is space
available for two sets of tanks and pump houses?  I've never seen a
high-rise sprinkler system fed from a site pump and tank.  I suppose a pump
and tank buried in plaza would be OK as the secondary but you would have to
engineer the entire secondary system to withstand the seismic event.  I've
always assumed this secondary supply is located inside the building.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell