The concept is that if there is an earthquake or similar incident that
disrupts municipal supply that there is a sufficient back-up supply.
The equation becomes simple once you embrace this notion: No single
disruption in one supply feed can disrupt the other supply feed.

On Wed, Feb 16, 2011 at 7:07 AM, Bill Brooks <[email protected]> wrote:
> What kind of high-rise building are you thinking about where there is space
> available for two sets of tanks and pump houses?  I've never seen a
> high-rise sprinkler system fed from a site pump and tank.  I suppose a pump
> and tank buried in plaza would be OK as the secondary but you would have to
> engineer the entire secondary system to withstand the seismic event.  I've
> always assumed this secondary supply is located inside the building.
>
> Bill Brooks
>
> William N. Brooks, P.E.
> Brooks Fire Protection Engineering Inc.
> 372 Wilett Drive
> Severna Park, MD 21146-1904
> 410-544-3620
> 410-544-3032 FAX
> 412-400-6528 Cell
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Shelton, Eric
> Sent: Wednesday, February 16, 2011 8:54 AM
> To: [email protected]
> Subject: RE: IBC 2006, section 903.3.5.2
>
> What about a situation where you had primary pump house and tank and a
> secondary pump house and tank "on-site".  Would you have to provide a
> separate underground service to your building from each pump house?  If
> you provided a secondary pump house and tank "on-site" and the primary
> was a city supply, could you tie the secondary underground from the pump
> house into the city supply outside?
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Jeff
> Hewitt
> Sent: Tuesday, February 15, 2011 5:14 PM
> To: [email protected]
> Subject: RE: IBC 2006, section 903.3.5.2
>
> The commentary to IBC 2009 clarifies this issue.
>
> An excerpt is as follows:
>
> "The text's specific wording that the secondary supply be "on-site"
> would
> preclude the use, for example, of a second connection to the municipal
> water
> supply remote from the primary connection to achieve compliance with
> this
> requirement."
>
>
>
>
>
> Jeff Hewitt, PE, SET, SFPE (Professional Member)
> Corporate Engineer
> Bi-State Fire Protection Corporation
>
> 241 Hughes Lane
> St. Charles, MO  63301
> 636-946-0011
> 636-946-5172 (fax)
> 314-574-6989 (cell)
>
> Fire Sprinklers Save lives.
> Can You Live Without Them?
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Shelton,
> Eric
> Sent: Tuesday, February 15, 2011 3:54 PM
> To: [email protected]
> Cc: Howell Taylor
> Subject: IBC 2006, section 903.3.5.2
>
> Posting this for a friend having technical difficulties ......
>
>
>
>
>
> IBC section 903.3.5.2 is about the provision of secondary water supply
> for high-rise buildings in certain seismic zones.  My question is, does
> the definition of secondary water supply include separate underground
> piping to feed the building or can the secondary water supply tie into
> the primary underground piping prior to entering the building or
> anywhere else on site.
>
>
>
> Eric J. Shelton, PE
>
> Senior Fire Protection Engineer
>
> AECOM Design
>
> Direct 540.857.3282
>
> AECOM
>
> 10 South Jefferson Street, Suite 1600
>
> Roanoke, Virginia 24011
> T 540.857.3100   F 540.857.3180
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to