What kind of high-rise building are you thinking about where there is space available for two sets of tanks and pump houses? I've never seen a high-rise sprinkler system fed from a site pump and tank. I suppose a pump and tank buried in plaza would be OK as the secondary but you would have to engineer the entire secondary system to withstand the seismic event. I've always assumed this secondary supply is located inside the building.
Bill Brooks William N. Brooks, P.E. Brooks Fire Protection Engineering Inc. 372 Wilett Drive Severna Park, MD 21146-1904 410-544-3620 410-544-3032 FAX 412-400-6528 Cell -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Shelton, Eric Sent: Wednesday, February 16, 2011 8:54 AM To: [email protected] Subject: RE: IBC 2006, section 903.3.5.2 What about a situation where you had primary pump house and tank and a secondary pump house and tank "on-site". Would you have to provide a separate underground service to your building from each pump house? If you provided a secondary pump house and tank "on-site" and the primary was a city supply, could you tie the secondary underground from the pump house into the city supply outside? -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Jeff Hewitt Sent: Tuesday, February 15, 2011 5:14 PM To: [email protected] Subject: RE: IBC 2006, section 903.3.5.2 The commentary to IBC 2009 clarifies this issue. An excerpt is as follows: "The text's specific wording that the secondary supply be "on-site" would preclude the use, for example, of a second connection to the municipal water supply remote from the primary connection to achieve compliance with this requirement." Jeff Hewitt, PE, SET, SFPE (Professional Member) Corporate Engineer Bi-State Fire Protection Corporation 241 Hughes Lane St. Charles, MO 63301 636-946-0011 636-946-5172 (fax) 314-574-6989 (cell) Fire Sprinklers Save lives. Can You Live Without Them? -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Shelton, Eric Sent: Tuesday, February 15, 2011 3:54 PM To: [email protected] Cc: Howell Taylor Subject: IBC 2006, section 903.3.5.2 Posting this for a friend having technical difficulties ...... IBC section 903.3.5.2 is about the provision of secondary water supply for high-rise buildings in certain seismic zones. My question is, does the definition of secondary water supply include separate underground piping to feed the building or can the secondary water supply tie into the primary underground piping prior to entering the building or anywhere else on site. Eric J. Shelton, PE Senior Fire Protection Engineer AECOM Design Direct 540.857.3282 AECOM 10 South Jefferson Street, Suite 1600 Roanoke, Virginia 24011 T 540.857.3100 F 540.857.3180 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)