Ed,
I don't remember who, but once upon a time I learned in a seminar that the way 
to approach this is to calc 1500 sq ft in the vicinity of the opening, and then 
apply the reduction elsewhere.  

Bob

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ed Kramer
Sent: Friday, March 11, 2011 11:43 AM
To: [email protected]
Subject: QR design area reduction

I've got a light hazard dining area with a 10'-6" ceiling which meets all the 
criteria for reducing the design area down to 912 sf.  Well, almost all the 
criteria.  There is one small 'atrium' with a 23' ceiling height.  The 'atrium' 
is only 6' x 11' and is protected by 1 sprinkler.  

 

Am I allowed to reduce the design area based on the 10'-6" ceiling height,
or must I calculate a full 1,500 sf?   Or more generically, how small must
an area of higher ceiling be in order to ignore it when applying section 
11.2.3.2.3?

 

Opinions?

 

Ed Kramer

Littleton, CO