When I asked about a small are similar to this with a sloped ceiling, I was
told that since the entire sloped area was encompassed in the remote area an
adjustment increase would not be required.
But, in this case I really don't know.  I know that yould literally reduce
the demand area everywhere else except where this pocket is at the least.
Therefore if your pocket area was closer to the riser, calc'ing 1500 sq ft
may not be as bad.

That is probably how I would look at it. If the high area was less than 32
sq ft, it may be small enough to ignore?
On Mar 11, 2011 2:50 PM, "Bobby Gillett" <[email protected]>
wrote:
> That is a good question; I have had situations like that where small
areas,
> like your atrium for example, were not in the most demanding remote area
and
> wondered whether or not I could apply the reduction. I am waiting to see
> more responses; due to the number of responses so far either everyone is
> busy or they are waiting patiently too.
>
>
>
> Bobby Gillett
>
> Sr. Project Manager
>
> Key Fire Protection, Inc.
>
> (731) 424-0130 office (731) 424-9285 fax
>
> (731) 267-4853 cell
>
> <mailto:[email protected]>
> [email protected]
>
>
>
>
>
> _____
>
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Ed Kramer
> Sent: Friday, March 11, 2011 12:43 PM
> To: [email protected]
> Subject: QR design area reduction
>
>
>
> I've got a light hazard dining area with a 10'-6" ceiling which meets all
> the criteria for reducing the design area down to 912 sf. Well, almost all
> the criteria. There is one small 'atrium' with a 23' ceiling height. The
> 'atrium' is only 6' x 11' and is protected by 1 sprinkler.
>
>
>
> Am I allowed to reduce the design area based on the 10'-6" ceiling height,
> or must I calculate a full 1,500 sf? Or more generically, how small must
> an area of higher ceiling be in order to ignore it when applying section
> 11.2.3.2.3?
>
>
>
> Opinions?
>
>
>
> Ed Kramer
>
> Littleton, CO
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _____
>
> No virus found in this message.
> Checked by AVG - www.avg.com
> Version: 10.0.1204 / Virus Database: 1497/3500 - Release Date: 03/11/11
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to