Waiting patiently too, but I do know 1) the reduction curve is based on height- the lower the ceiling the faster the heat travels across it so the faster the heads activate and the smaller the area of activation, so any 912 SF of heads at 10-6 will work. 2) the 4th parameter for QR Reduction is no unprotected ceiling pockets greater than 32 SF. If the 'atrium' is a protected ceiling pocket, I see what you mean by meeting all the requirements. It sounds like your main ceiling is 10-6, but contains a 'ceiling feature', that is protected.
-----Original Message----- From: Bobby Gillett [mailto:[email protected]] Sent: Friday, March 11, 2011 2:51 PM To: [email protected] Subject: RE: QR design area reduction That is a good question; I have had situations like that where small areas, like your atrium for example, were not in the most demanding remote area and wondered whether or not I could apply the reduction. I am waiting to see more responses; due to the number of responses so far either everyone is busy or they are waiting patiently too. Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell <mailto:[email protected]> [email protected] _____ From: [email protected] [mailto:[email protected]] On Behalf Of Ed Kramer Sent: Friday, March 11, 2011 12:43 PM To: [email protected] Subject: QR design area reduction I've got a light hazard dining area with a 10'-6" ceiling which meets all the criteria for reducing the design area down to 912 sf. Well, almost all the criteria. There is one small 'atrium' with a 23' ceiling height. The 'atrium' is only 6' x 11' and is protected by 1 sprinkler. Am I allowed to reduce the design area based on the 10'-6" ceiling height, or must I calculate a full 1,500 sf? Or more generically, how small must an area of higher ceiling be in order to ignore it when applying section 11.2.3.2.3? Opinions? Ed Kramer Littleton, CO _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _____ No virus found in this message. Checked by AVG - www.avg.com Version: 10.0.1204 / Virus Database: 1497/3500 - Release Date: 03/11/11 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)