That's because it is only referring to hose stream allowance and duration.  But 
the rooms cannot be adjacent so to break a kitchen into two 400 sq. ft rooms 
would mean there would have to be a room of lesser hazard between them.  Doubt 
you're going to be able to break up a kitchen that way and make it still work.  
Plus that reference doesn't mean you can change the occupancy to a lesser 
occupancy, Kitchen still equals OH no matter what.  It will never be an LH.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Joel Chaim
Sent: Monday, April 04, 2011 2:42 PM
To: [email protected]
Subject: RE: Design solution needed

Yes but it does not say anything about density.

 

From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Monday, April 04, 2011 2:36 PM
To: [email protected]
Subject: RE: Design solution needed

 

Maybe referring to 12.7.2?

Craig L. Prahl, CET  
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Monday, April 04, 2011 2:27 PM
To: [email protected]
Subject: Re: Design solution needed

where are you getting the idea that you can divide the kitchen into 
two 400 sf compartments and legitimately call it light hazard?  Pipe 
type and hose demand is allowed to use LH (though for hose demand, the 
rooms can not be adjacent so that nixes reducing it).

Roland

On Apr 4, 2011, at 10:40 AM, Joel Chaim wrote:

> I'm thinking of offering them to divide the kitchen area into 2 
> compartments
> less than 400 sq ft. this way we can utilize the same hazard as the 
> dining
> area my question can we lower the density to .10 as well because 
> NFPA states
> that regardless if utilize the hose demand or not you still need to 
> calc.
> 1500 sq ft. even the room is less.
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 

  _____  

No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1209 / Virus Database: 1500/3549 - Release Date: 04/04/11

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to