That's because it is only referring to hose stream allowance and duration. But the rooms cannot be adjacent so to break a kitchen into two 400 sq. ft rooms would mean there would have to be a room of lesser hazard between them. Doubt you're going to be able to break up a kitchen that way and make it still work. Plus that reference doesn't mean you can change the occupancy to a lesser occupancy, Kitchen still equals OH no matter what. It will never be an LH.
Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SCĀ 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Joel Chaim Sent: Monday, April 04, 2011 2:42 PM To: [email protected] Subject: RE: Design solution needed Yes but it does not say anything about density. From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Monday, April 04, 2011 2:36 PM To: [email protected] Subject: RE: Design solution needed Maybe referring to 12.7.2? Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Roland Huggins Sent: Monday, April 04, 2011 2:27 PM To: [email protected] Subject: Re: Design solution needed where are you getting the idea that you can divide the kitchen into two 400 sf compartments and legitimately call it light hazard? Pipe type and hose demand is allowed to use LH (though for hose demand, the rooms can not be adjacent so that nixes reducing it). Roland On Apr 4, 2011, at 10:40 AM, Joel Chaim wrote: > I'm thinking of offering them to divide the kitchen area into 2 > compartments > less than 400 sq ft. this way we can utilize the same hazard as the > dining > area my question can we lower the density to .10 as well because > NFPA states > that regardless if utilize the hose demand or not you still need to > calc. > 1500 sq ft. even the room is less. > _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _____ No virus found in this message. Checked by AVG - www.avg.com Version: 10.0.1209 / Virus Database: 1500/3549 - Release Date: 04/04/11 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)