We had 2 of these a the City Center project, one each for the 8" high
pressure and 10" low pressure loops around the site.

>From what I remember, on the discharge side of the pump just after the tee
creating the loop (within the central plant - heated space), we installed 2
check valves and two outlets (circulating pump in & out).  Even with this
arangement, created and approved by the PE consultants and approved by the
AHJ, we still had to add insulation around the pipe at varing thicknesses in
different areas.

There was an entire report on heat loss/gain for each area that the pipe
passed through, projected air current speeds, how many feet of pipe had to
be within heated spaces, GPM circulation requirements, and even how many
feet of pipe could be exposed to a non-circulating condition (feeds for
standpipes into stairwells, bulk mains to upper levels) that we had to
comply with.


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Damien
Shannon
Sent: Wednesday, April 06, 2011 5:40 AM
To: [email protected]
Subject: Firewater Circulation Pump

Dear Forum,

Wondering if anyone can share knowledge/experience in regards to 'Firewater
Circulation Pump' arrangements as a solution to freeze protection.

Personally never heard of them before today but we have an enquiry in from a
facility that has one that is in place several years. 10" externally looped
main aboveground around a facility (approx 1500' worth). However it is not
performing as it was intended as he has had freeze ups. There are some
dead-end pipes feeding FHVs off this loop which I can't even see as being
feasible with the concept.

Below is a link that discusses the topic (page 60), though it doesn't have
arrangement details/schematic or such. Can anyone provide info or refer a
source that would provide details for the valving/arrangement.

Any insight would be appreciated.

Damien Shannon
Provincial Sprinkler Company Ltd.
Unit 4, Cork Airport Industrial Estate
Kinsale Road, 
Cork, Ireland.
Tel: (021) 4965058
Fax: (021) 4317425

http://books.google.ie/books?id=1o6-H-ajj5oC&pg=PA60&dq=fire+water+recircula
tion+pumps&hl=en&ei=kc1sTfHELJSChQeQ2IWPDA&sa=X&oi=book_result&ct=result&res
num=1&ved=0CD4Q6AEwAA#v=onepage&q&f=false




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to