Hi Craig,

Thank you for the reply.

I also find this concept 'unorthodox' as it is something I have never heard
of before. However, many times in the past I have thought something to not
be acceptable only to find out that it is quite the norm somewhere. Wasn't
sure if that was maybe the case here. The fact that it was mentioned in that
book 'Fire Fighting Pumping Systems at Industrial Facilities' by Dennis P.
Nolan made me think that thing was a procedure that was being provided
somewhere and that there would be a Standard outside of NFPA 20 that
provided requirements for installation of such. If there was another
Standard that provided for such an installation the AHJ might have been able
to accept it based on that Standard. They somehow got approval from their
insurers first day as this is an operating facility.

The fact that he has freeze up certainly indicates that it is not working
but is possibly because of incorrect original installation (valving
arrangement) or non functioning valve... 

If there was a way of installing this type of arrangement correctly for the
loop, the dead ends could possibly be heat traced and lagged and would not
have been nearly as involved/expensive as heat tracing and lagging the
entire loop which is what seems to be their only other feasible option.

Thanks again for the input. 

Damien.



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, April 06, 2011 9:12 AM
To: [email protected]
Subject: RE: Firewater Circulation Pump

The only recirc I've ever heard of had to do with recirculating water at the
fire water storage tank as a means to prevent freezing of water within the
tank. (Ref. NFPA 22) 

I've had this proposed by an owner who wanted to do some unorthodox and
questionable things but we turned it down as there was no reference to the
process in any Standard.

Obviously if they've had freeze-ups the method is unsatisfactory in
providing protection of the pipe against freezing.

The only way any recirc can work is for the system to be looped so if for no
other reason, the presence of dead- end legs should have taken this option
off the table. 

There is no mention of the practice in the NFPA Handbook nor NFPA 24.  That
being the case how would an AHJ accept this as a proven method to protect
the system against freezing?



Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Damien
Shannon
Sent: Wednesday, April 06, 2011 8:40 AM
To: [email protected]
Subject: Firewater Circulation Pump

Dear Forum,

Wondering if anyone can share knowledge/experience in regards to 'Firewater
Circulation Pump' arrangements as a solution to freeze protection.

Personally never heard of them before today but we have an enquiry in from a
facility that has one that is in place several years. 10" externally looped
main aboveground around a facility (approx 1500' worth). However it is not
performing as it was intended as he has had freeze ups. There are some
dead-end pipes feeding FHVs off this loop which I can't even see as being
feasible with the concept.

Below is a link that discusses the topic (page 60), though it doesn't have
arrangement details/schematic or such. Can anyone provide info or refer a
source that would provide details for the valving/arrangement.

Any insight would be appreciated.

Damien Shannon
Provincial Sprinkler Company Ltd.
Unit 4, Cork Airport Industrial Estate
Kinsale Road, 
Cork, Ireland.
Tel: (021) 4965058
Fax: (021) 4317425

http://books.google.ie/books?id=1o6-H-ajj5oC&pg=PA60&dq=fire+water+recircula
tion+pumps&hl=en&ei=kc1sTfHELJSChQeQ2IWPDA&sa=X&oi=book_result&ct=result&res
num=1&ved=0CD4Q6AEwAA#v=onepage&q&f=false




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to