Brian,
I use HydraCalc also and find it the easiest to run separate calcs for
each system that have a common calc point in both.
Get each calc close to 1 PSI of each other at that common point and then
use "cut and paste" to add the rack to the overhead calc.  I can then
run a combined calc that is fairly close to being balanced.  When I try
to run a combined calc right from the start I find it much harder to
balance it.
Dewayne

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brian
Harris
Sent: Wednesday, April 20, 2011 9:07 AM
To: [email protected]
Subject: Balancing Rack Calc's

I knew sooner or later my luck would run out and I'd have a job with
racks, yes ladies and gentlemen this is the first time I've had to do an
in rack system. I've searched through code, searched past archives, and
still am not all warm and fuzzy with my conclusion, if someone would be
so kind as to either give me either an amen or send me to the corner
with a dunce cap I would greatly appreciate it.

 

I have done my overhead calc's, done my rack calc's, they are balanced
to within .5 psi of each other at a common point on the riser. My
question is
this: does it matter which calc has the higher of the two pressures? The
reason I ask is when it comes to the combined calc and you balance the
flow at the common point on the riser I have tried two scenarios, if the
higher pressure is on the rack system and you plug in the "balance"
formula I get
981 gallons I need to add to the rack system which will work. If I tweak
a couple things and the overhead system is the higher pressure and plug
that into the "balance" formula I get 181 gallons that I need to add to
the overhead system and that will not work. What is the consensus of the
forum?

 

Brian Harris

First Defense Fire Protection

11957 Ramah Church Road

Huntersville, NC 28078

Phone: 704.948.3506

Fax: 704.948.3507

Nicet # 128476

 





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17320)
http://www.pctools.com/ =======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to