the room is a high school music room with 90 2X4  ceiling panels and only 16 of 
them are
eggcrate panels.  The 16 eggcrate 2X4 panels have a 40% opening per panel.  We 
have 
pendants protecting the room but Fire Marshall thinks we need uprights.

Gayle Knowles, SET
Project Manager
Kaufman Fire Protection Systems. Inc. 
PH:505-884-2447


 
> From: [email protected]
> To: [email protected]
> Date: Wed, 1 Jun 2011 13:58:56 -0600
> Subject: RE: openings in ceiling grid
> 
> Since they are open eggcrate panels, are they using the space above for a 
> return or supply plenum? 
> 
> Craig L. Prahl, CET 
> Fire Protection 
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension 74102
> [email protected]
> 
> 
> 
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of GAYLE KNOWLES
> Sent: Wednesday, June 01, 2011 3:56 PM
> To: sprinklerforum
> Subject: openings in ceiling grid
> 
> 
> Sorry if this has come up before....we have a music room with drop in ceiling 
> 2X4 tile, but
> a few of the tiles are an eggcrate style(40% open per tile). Fire Marshall 
> would like us to direct him to the specific
> section of NFPA 13 (2010) that allows us not to put uprights above this room. 
> We can only find
> section 8.15.1.2.1.1 explanation in handbook stating "evaluation of size and 
> number of openings
> in relation to the overall area of the ceiling is important". This may be a 
> decision he as AHJ will
> need to make. Structure above ceiling, of course, non-combustible.
> 
> Thanks for any help to keep us from adding uprights in this room
> 
> Gayle Knowles, SET
> Project Manager
> Kaufman Fire Protection Systems. Inc. 
> PH:505-884-2447
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
                                          
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to