16 seems excessive for Return Air, It might be for supply, to keep ambient
noise down, by using very low velocity from the "Plenum above the ceiling,
but if this is an existing classroom, the chance is more likely that these
"Egg Crate" panels were what they had on hand, when the solid panels got wet
or were broken at some point. If you can find the original HVAC drawings
they should tell you what was original design. (An 800 SF classroom would
normally only have about 4 panels for return air.)

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of GAYLE KNOWLES
Sent: Wednesday, June 01, 2011 2:27 PM
To: sprinklerforum
Subject: RE: openings in ceiling grid


the room is a high school music room with 90 2X4  ceiling panels and only 16
of them are
eggcrate panels.  The 16 eggcrate 2X4 panels have a 40% opening per panel.
We have 
pendants protecting the room but Fire Marshall thinks we need uprights.

Gayle Knowles, SET

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to