Sounds like the room is about 720 sf.  Typical airflow for this space
would be in the range of 1500 cfm.  One 2x4 eggcrate grille can handle
in excess of 2500 cfm.  Not sure why the room needs 16 panels.  Could be
an acoustical treatment?  Seems like an odd way to improve acoustics if
that is what the purpose is.  Suggest reducing the number of panels to
amount required for return air.  If panels are required for acoustics,
coverage above the ceiling is probably required.


Kevin D. Schaefer PE LEED(r)AP
Managing Principal

40 Beaver Street
Albany, New York 12207
p: 518.463.8068 x269
f: 518.463.8069 
www.csarchpc.com



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of GAYLE
KNOWLES
Sent: Wednesday, June 01, 2011 5:11 PM
To: sprinklerforum
Subject: RE: openings in ceiling grid


This is a brand new high school.  We are sending thru an RFI to find out
what these panels are for.
they are scattered throughout the room with no apparent pattern.  Will
let you know.  Thanks

Gayle Knowles, SET
Project Manager
Kaufman Fire Protection Systems. Inc. 
PH:505-884-2447


 
> From: [email protected]
> To: [email protected]
> Subject: RE: openings in ceiling grid
> Date: Wed, 1 Jun 2011 14:50:44 -0600
> 
> 16 seems excessive for Return Air, It might be for supply, to keep
ambient
> noise down, by using very low velocity from the "Plenum above the
ceiling,
> but if this is an existing classroom, the chance is more likely that
these
> "Egg Crate" panels were what they had on hand, when the solid panels
got wet
> or were broken at some point. If you can find the original HVAC
drawings
> they should tell you what was original design. (An 800 SF classroom
would
> normally only have about 4 panels for return air.)
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of GAYLE
KNOWLES
> Sent: Wednesday, June 01, 2011 2:27 PM
> To: sprinklerforum
> Subject: RE: openings in ceiling grid
> 
> 
> the room is a high school music room with 90 2X4 ceiling panels and
only 16
> of them are
> eggcrate panels. The 16 eggcrate 2X4 panels have a 40% opening per
panel.
> We have 
> pendants protecting the room but Fire Marshall thinks we need
uprights.
> 
> Gayle Knowles, SET
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email
to:[email protected]
> (Put the word unsubscribe in the subject field)
                                          
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to