I seemed to recall and now have found something that may apply here. NFPA 291 on Fire Flow Testing of Hydrants: 4.9.1 If a pitot tube is not available for use measure the hydrant discharge, a 50 or 60 psi gauge tapped into a hydrant cap can be used. 4.9.2 The hydrant cap with gauge attached is placed on one outlet, and the flow is allowed to take place through the other outlet as the same elevation. 4.9.3 The readings obtained from a gauge so located, and the readings obtained from a gauge on a pitot tube held in the stream, are approximately the same.
The physics are that the total energy of the flowing water is converted from static pressure (at the gauge so located) to velocity pressure as the stream discharges. So, this exercise is really about identifying your effective point of the test for purposes of calcing your available supply. You would need to calc the friction loss from the main through the tee, gate valve if present, the hydrant valve, up the barrel and to the gauge based on the flow through the hydrant. That friction loss is then added to your "residual" pressure, which is "approximately the same" as your pitot pressure, to get your available supply in the main. Of course, adjust for the elevation difference between your test hydrant and the base of riser, or other reference point, for your system. Dave David A. de Vries, P.E., CSP Firetech Engineering Incorporated --- On Fri, 7/22/11, Vince Sabolik <[email protected]> wrote: From: Vince Sabolik <[email protected]> Subject: RE: Convert pitot to actual residual?? To: [email protected] Date: Friday, July 22, 2011, 12:40 PM Ok -- Let me lay it out - I have two flow tests; one from a branch main and one from a supply main. Both 'residual' are actually pitot readings, about 300 ft apart through a 6" main. I'm using the test with the lower residual pressure. These tests are: 52 / 31 / 924 and 51 / 9 / 503 I'm pretty sure that I've come up with a residual pressure but was looking for another method (one that only the one-piece test kit people know, apparently) to check me. Anyone that feels like it, play away. And if any Pollard Hydrant Pro or Hose Monster folks are looking in, tell me the secret! Vince Vince Sabolik, West Tech Fire Protection, Inc. 11351 Pearl Road / Strongsville, Ohio 44136 440 238-4800 Fax 440 238-4876 ____________________________________________________________________ _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)