I seemed to recall and now have found something that may apply here.  NFPA 291 
on Fire Flow Testing of Hydrants:
 
4.9.1  If a pitot tube is not available for use measure the hydrant discharge, 
a 50 or 60 psi gauge tapped into a hydrant cap can be used.
 
4.9.2  The hydrant cap with gauge attached is placed on one outlet, and the 
flow is allowed to take place through the other outlet as the same elevation.
 
4.9.3  The readings obtained from a gauge so located, and the readings obtained 
from a gauge on a pitot tube held in the stream, are approximately the same.

The physics are that the total energy of the flowing water is converted from 
static pressure (at the gauge so located) to velocity pressure as the stream 
discharges.  So, this exercise is really about identifying your effective point 
of the test for purposes of calcing your available supply.  You would need to 
calc the friction loss from the main through the tee, gate valve if present, 
the hydrant valve, up the barrel and to the gauge based on the flow through the 
hydrant.  That friction loss is then added to your "residual" pressure, which 
is "approximately the same" as your pitot pressure, to get your available 
supply in the main.  Of course, adjust for the elevation difference between 
your test hydrant and the base of riser, or other reference point, for your 
system.
 

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 




--- On Fri, 7/22/11, Vince Sabolik <[email protected]> wrote:


From: Vince Sabolik <[email protected]>
Subject: RE: Convert pitot to actual residual??
To: [email protected]
Date: Friday, July 22, 2011, 12:40 PM


Ok --

Let me lay it out -

I have two flow tests; one from a branch main and one from a supply main.
Both 'residual' are actually pitot readings, about 300 ft apart through a 6" 
main.

I'm using the test with the lower residual pressure.

These tests are:

52 / 31 / 924
and
51 / 9 / 503

I'm pretty sure that I've come up with a residual pressure but was looking for 
another
method (one that only the one-piece test kit people know, apparently) to check 
me.

Anyone that feels like it, play away.  And if any Pollard Hydrant Pro or Hose 
Monster folks are
looking in, tell me the secret!


                                                                                
               Vince



Vince Sabolik, West Tech Fire Protection, Inc.
11351 Pearl Road / Strongsville, Ohio 44136       440 238-4800     Fax 440 
238-4876
____________________________________________________________________


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to