2007 edition NFPA 13:22.4.2.3

P(normal) = P(total) - P(velocity)

Since you have two unknowns and only one equation...you cannot solve with only 
the velocity pressure (pitot reading).


Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Ron Greenman [mailto:[email protected]] 
Sent: Friday, July 22, 2011 11:36 AM
To: [email protected]
Subject: Re: Convert pitot to actual residual??

If there was, and maybe there is but I don't know of any, a regular
mathematical relationship between velocity pressures and residual pressures
then yes. Our little log graphs tend to fool us visually because the picture
you conjure in your head shows a nice straight line on the graph. Unless
you're a mathematician (and I'm not) I think it's difficult
to unconsciously remember that the graph is not regular and the straight
lines are curves so everything seems proportional and regular but is not.
i'm of the belief that you need to read a residual during a flow test to get
a residual baseline for the other formulae to work. But then again I'm on
a logarithmic ignorance graph wherein I find that I know less than I thought
on a progressively increasing rate over time. Since everything can be
modeled these days (or at least that's what the purveyors are telling us)
there ought to be a way. I did once get water availability info that was
just impossible and managed to bully the water guy into giving me a copy of
the test instead of just the final data. It was the same problem in that the
tester had recorded the same numbers for residual and velocity and though
I'll be open and say it's possible I'd think the chances were one in
infinity minus one. They re-did the test and the numbers made sense. I think
you have an opportunity to help your ignorant purveyor (Did I say that out
loud? I'm sorry. I have the upmost respect for water purveyors and backflow
specialists being competent in their code interpretation abilities,
knowledge of hydrostatics and hydrokinetics, and overall common sense.) to
learn how to do these tests and perhaps make a little money.

On Fri, Jul 22, 2011 at 8:07 AM, Vince Sabolik <[email protected]> wrote:

> Ron,
>
> Ron,
>
> Yeah figured so. I just thought that someone may have had one of those
> 'rule of thumb' thingys laying around.
>
> Seems to me THAT should be possible, no?
>
> I just wanted this to guestimate the design ahead of doing another test.
>
> BTW, sorry about the double posts. I'm having an argument with me this
> morning.
>
>
>
>
> At 10:58 AM 7/22/2011, you wrote:
>
>> Vince,
>>
>> Since you don't have a residual, which is the left over energy in the
>> system
>> measured in psi at the non-flowing hydrant, while flowing through that
>> circular orifice you're screwed and the test has to be re-done. Once you
>> have actual flow and residual you can calculate flow at any residual
>> pressure (changes with the size of orifice) or residual at any flow.
>> Unfortunately static minus velocity (the pitot reading) doesn't equal
>> residual. Life and understanding the world would be so much easier if it
>> ran
>> on magic and religion instead of physics.
>>
>> Vince Sabolik, West Tech Fire Protection, Inc.
>>
> 11351 Pearl Road / Strongsville, Ohio 44136       440 238-4800     Fax 440
> 238-4876
> ______________________________**______________________________**________
>
>
> ______________________________**_________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.**org <[email protected]>
> http://fireball.firesprinkler.**org/mailman/listinfo/**sprinklerforum<http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum>
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:Sprinklerforum-request@**
> firesprinkler.org <to%[email protected]>
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to