>I think section 8.5.2.1.1-2 (NFPA 13 07ed) supports your thinking when 
>determining the area of the sprinkler.

Part (b) of that section states "Choose the larger of either twice the distance 
to the wall or obstruction of the distance to the next sprinkler"

Twice the distance to the wall is 10', the distance between the sprinklers is 
12'-6". Per that section, L = 12'-6". S is 12', therefore SxL = 150, as Mike 
stated. 

That was looking at it from the 12 x 10 side. If you look at it from the 8 x 15 
side, twice the distance is 15 ft and the distance between sprinklers is 13'-6. 
Therefore that side is OK, but the other is not.

n'est pas?


Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com