"I worry about the clients as they're multi-handicapped adults, some were 
dropped off there as infants."

They are nowhere near self-rescuing, so it would be an I-2 classification. MA 
Code (section 421) defines a Group Residence as being occupied by residents 
that capable of self-preservation. The exact classification needs to be further 
defined. How many residents are there in the building? Five or fewer and it 
could be classified as Residential per MA Code, but that would need to be 
further defined. Do they have staff living at the facility or do people work 
there in shifts 24/7? If the latter, it is a nursing home. I did a system in 
western CT for virtually the same occupancy a few years ago and fought this 
battle personally.

A PE would probably have to evaluate and sign off on any change in occupancy 
classification and decrease in coverage. Also, he/she need to be willing to 
accept the liability for such a judgement. Don't call me. 