Joel,
You need to determine the fire protection sprinkler flow. Is 15,000 gallons
going be enough?
Then you need to discuss with the engineer who designed the original
domestic and understand how the domestic system works. How is the tank being
refilled during the day?
If the supply is going to be used for sprinkler demand then the water supply
cannot be drawn down below what is required for the sprinkler system.
Regards,
G. Tim Stone
G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services
117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638 TEL: (802) 434-2968 Fax: (802) 434-4343
[email protected]
> -----Original Message-----
> From: [email protected] [mailto:sprinklerforum-
> [email protected]] On Behalf Of Joel Chaim
> Sent: Tuesday, May 08, 2012 11:40 AM
> To: [email protected]
> Subject: RE: domestic demand per nfpa 13
>
> Would a solenoid valve be approved in such a situation?
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Ron
> Greenman
> Sent: Tuesday, May 08, 2012 11:40 AM
> To: [email protected]
> Subject: Re: domestic demand per nfpa 13
>
> You could probably use the plumbing code tables (that's where the 13R
> stuff comes from) for determining the demand.
>
> On Tue, May 8, 2012 at 8:34 AM, Joel Chaim
> <[email protected]>wrote:
>
> > I have a job that has a 15000 gallon tank for 72 buildings and they
> > want to use the existing tank for fire sprinkler as well.
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of Roland
> > Huggins
> > Sent: Tuesday, May 08, 2012 11:15 AM
> > To: [email protected]
> > Subject: Re: domestic demand per nfpa 13
> >
> > Why are you asking since it is normally not included in the
> calculations.
> >
> > Roland
> >
> >
> > On May 8, 2012, at 8:05 AM, Joel Chaim wrote:
> >
> > > Is there a table for domestic demand as per NFPA. 13? I only saw it
> > > under NFPA 13 R.
> > >
> > >
> > >
> > >
> > >
> > > -------------- next part -------------- An HTML attachment was
> > > scrubbed...
> > > URL:
> > >
> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/at
> > > ta chments/20120508/4a03127a/attachment.html
> > > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>
> They are happy men whose natures sort with their vocations. -Francis
> Bacon, essayist, philosopher, and statesman (1561-1626)
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attac
> hment
> s/20120508/80b41200/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum