I find it curious that if you have a 4-story residential building and design
it to NFPA 13R, you would have to include the domestic demand but take the
same building and add a garage in the basement and commercial space on the
ground floor and now you don't have to include the domestic demand because
NFPA 13 does not require it.  

In such buildings with a combined water entry, I've been adding the domestic
demand in accordance with the guidelines of 13R.

David
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Tuesday, May 08, 2012 11:15 AM
To: [email protected]
Subject: Re: domestic demand per nfpa 13

Why are you asking since it is normally not included in the  
calculations.

Roland


On May 8, 2012, at 8:05 AM, Joel Chaim wrote:

> Is there a table for domestic demand as per NFPA. 13? I only saw it  
> under
> NFPA 13 R.
>
>
>
>
>