72 building? Apartment buildings? How many units? Turning off domestic to a building during a fire is one solution. But you can't turn off domestic supply to a 1,000 people because there is a fire somewhere. How many water heaters do you empty, the refill when service is restored. Adequate infrastructure is part of development. If my presumption of twelve units per apartment building, and population estimate are ballpark, then the water in storage on a per capita basis is less than towns of 20,000 - 85,000 persons store. It follows that a smaller population needs more per capita than a larger population. Of course if they really have ability to say, pump 2,500 gpm on a continuous basis for several hours, and the tank is elevated to operate as a standpipe, as the term is used in the hydroelectric industry, then the conversation is different. I think we need more information about complex, size and height of buildings, access, available FD response, evaluation of possibility of building to building spread. Then we need a description of the water supply.
In a bidder design eorld Sent from my Motorola ATRIX™ 4G on AT&T -----Original message----- From: Art Tiroly <[email protected]> To: [email protected] Sent: Tue, May 8, 2012 16:48:43 GMT+00:00 Subject: RE: domestic demand per nfpa 13 I see a bigger problem, keeping the tank full during peak domestic demands. What refills the storage tank? How much do you need for sprinkler demand. Does the domestic have pumping supply? Is that reliable for sprinkler? Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Joel Chaim Sent: Tuesday, May 08, 2012 11:40 AM To: [email protected] Subject: RE: domestic demand per nfpa 13 Would a solenoid valve be approved in such a situation? -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Ron Greenman Sent: Tuesday, May 08, 2012 11:40 AM To: [email protected] Subject: Re: domestic demand per nfpa 13 You could probably use the plumbing code tables (that's where the 13R stuff comes from) for determining the demand. On Tue, May 8, 2012 at 8:34 AM, Joel Chaim <[email protected]>wrote: > I have a job that has a 15000 gallon tank for 72 buildings and they > want to use the existing tank for fire sprinkler as well. > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Roland > Huggins > Sent: Tuesday, May 08, 2012 11:15 AM > To: [email protected] > Subject: Re: domestic demand per nfpa 13 > > Why are you asking since it is normally not included in the calculations. > > Roland > > > On May 8, 2012, at 8:05 AM, Joel Chaim wrote: > > > Is there a table for domestic demand as per NFPA. 13? I only saw it > > under NFPA 13 R. > > > > > > > > > > > > -------------- next part -------------- An HTML attachment was > > scrubbed... > > URL: > > <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/at > > ta chments/20120508/4a03127a/attachment.html > > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment s/20120508/80b41200/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120508/e31e9d17/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum