The use of an electrically operated solenoid valve would require the control 
circuits to be monitored/supervised from the Fire Protection system otherwise 
there would be no security of valve closure. Must be fail-safe operation.

Another way that we use in NZ would be to control the domestic/commercial 
takeoff with an hydraulic control valve(Clayton or similar) piloted from the 
Sprinkler system so that when the sprinkler operates it closes the other 
takeoff by the system dropping to minimum design pressure.
Isolation and testing of this hydraulic shut-off valve would normally be in the 
sprinkler valve house. Ideally the control valve should be in the valve house 
as well.

Without knowing the details of the site it is difficult to follow what is 
needed, but the simplest way is to have the domestic outlet from tank above the 
storage volume for sprinklers then run each feed pipe separately. If the 
sprinklers and domestic feeds are off the same main at some distance from the 
tanks then individual control of the domestic takeoffs is necessary. 

Russell Gregory
Christchurch, New Zealand
e-mail [email protected]
-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Joel Chaim
Sent: Wednesday, 9 May 2012 8:04 AM
To: [email protected]
Subject: RE: domestic demand per nfpa 13

Domestic service while there is fire is not an issue in this situation. I'm 
just looking for the right solenoid valve, it’s a 2" outdoor that we are 
looking for 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bruce Verhei
Sent: Tuesday, May 08, 2012 2:47 PM
To: [email protected]
Subject: RE: domestic demand per nfpa 13

....bidder design world sprinklers are all. But on a fire safety analysis for a 
new project they are only a part of the picture. 


Sent from my Motorola ATRIX™ 4G on AT&T

-----Original message-----
From: Bruce Verhei <[email protected]>
To: [email protected]
Sent: Tue, May 8, 2012 18:41:09 GMT+00:00
Subject: RE: domestic demand per nfpa 13

72 building? Apartment buildings?  How many units? Turning off domestic to a 
building during a fire is one solution.  But you can't turn off domestic supply 
to a 1,000 people because there is a fire somewhere.  How many water heaters do 
you empty,  the refill when service is restored.
Adequate infrastructure is part of development.  If my presumption of twelve 
units per apartment building, and population estimate are ballpark,  then the 
water in storage on a per capita basis is less than towns of 20,000 - 85,000 
persons store. It follows that a smaller population needs more per capita than 
a larger population.  Of course if they really have ability to say, pump 2,500 
gpm on a continuous basis for several hours, and the tank is elevated to 
operate as a standpipe, as the term is used in the hydroelectric industry, then 
the conversation is different.  
I think we need more information about complex,  size and height of buildings, 
access,  available FD response, evaluation of possibility of building to 
building spread. Then we need a description of the water supply.

In a bidder design eorld


Sent from my Motorola ATRIX™ 4G on AT&T

-----Original message-----
From: Art Tiroly <[email protected]>
To: [email protected]
Sent: Tue, May 8, 2012 16:48:43 GMT+00:00
Subject: RE: domestic demand per nfpa 13

I see a bigger problem, keeping the tank full during peak domestic demands.
What refills the storage tank? How much do you need for sprinkler demand.
Does the domestic have pumping supply? Is that reliable for sprinkler?


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Joel Chaim
Sent: Tuesday, May 08, 2012 11:40 AM
To: [email protected]
Subject: RE: domestic demand per nfpa 13

Would a solenoid valve be approved in such a situation? 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Tuesday, May 08, 2012 11:40 AM
To: [email protected]
Subject: Re: domestic demand per nfpa 13

You could probably use the plumbing code tables (that's where the 13R stuff 
comes from) for determining the demand.

On Tue, May 8, 2012 at 8:34 AM, Joel Chaim
<[email protected]>wrote:

> I have a job that has a 15000 gallon tank for 72 buildings and they 
> want to use the existing tank for fire sprinkler as well.
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Roland 
> Huggins
> Sent: Tuesday, May 08, 2012 11:15 AM
> To: [email protected]
> Subject: Re: domestic demand per nfpa 13
>
> Why are you asking since it is normally not included in the calculations.
>
> Roland
>
>
> On May 8, 2012, at 8:05 AM, Joel Chaim wrote:
>
> > Is there a table for domestic demand as per NFPA. 13? I only saw it 
> > under NFPA 13 R.
> >
> >
> >
> >
> >
> > -------------- next part -------------- An HTML attachment was 
> > scrubbed...
> > URL:
> > <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/at
> > ta chments/20120508/4a03127a/attachment.html
> > >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120508/80b41200/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120508/e31e9d17/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120508/29400f4f/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to