Having trouble finding my stone tablets but nonetheless, if the intent was for in-racks to have a 30% increase, it would say so in the in- rack section. Just like the 7 sprinkler on a single BL is 7 sprinklers for both wet-pipe and dry-pipe as well as pipe schedule being the same for both. So when we hear Andy Rooney's line - Have you ever wondered - just say no.

For those still squirming it might be worth noting that the vertical swoosh up the flue of a rack and slow horizontal spread is nothing like the horizontal interface with the fire regarding delays between the two systems. Also as Bill Thomas pointed out, the flame can be inches away from an in-rack sprinkler without it activating. Another hugely different aspect from horizontal interaction. As already said - apples and oranges.

NFPA caveat for TC members to be applied regarding this not to be considered anything official from NFPA

Roland

On May 31, 2012, at 1:51 PM, George Church wrote:

But to answer your original post, Brad, YES, the 30% increase is for the anticipated fire growth due to the delay in water delivery.

I won't argue that an engineered solution as Scott F suggests isn't a great idea, but for those of us not entitled to an opinion, we look to #13 and we see how many sprinklers on how many levels at an end head pressure, and we flow em, balance to the roof with its 30% increase, and run with the minimum consensus prescriptive answer already there. Our building code, IBC as adopted by PA, doesn't require us to read into the standard and GUESS if the TC contemplated the situation or didn't-. That's what we do here, throwing the combined brainpower of ideas synergistically propelling us toward bs or the right answer, depending on the day, until those who either KNOW the TC intent (and might have membership on Stds Council?) tell us some background, or what's in the works.

But for those of us with CET rather than PE or FPE, what's written in 13 is what we follow. If it says flow 6 sprinklers on each of two levels, that's twelve sprinklers, not eight and eight.

BTW, has anyone noticed a dramatic difference in the ignorance level of some of the Linked-In Group questions (compared to our little forum here)? I need to stay off them- if you've worked with FM Global, for example, would you agree with the guy who said he wondered how FM could get away with strong-arming American businesses with whatever was good for FM without a care about how much it cost the insured, and he hoped for the pendulum of intelligent design to swing the other way? Jeez, if you know anything about FM, they DO know a little about proper fire protection, they DO actually test things and develop valid criteria, I'll stop here since I'll assume I'm preaching to the choir. I'm not saying I agree with everything FM does, but I sure don't think their typical customer is strong-armed like a bunch of cowering small shopkeepers with the mob selling protection in their neighborhood, there are some reasonably intelligent people in risk management looking at the dollars invested into protecting their assets. Rant <OFF>


George L.  Church, Jr., CET
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] [mailto:[email protected] ] On Behalf Of [email protected]
Sent: Thursday, May 31, 2012 3:48 PM
To: [email protected]
Subject: RE: dry-pipe with in-rack/ceiling protection of Class IV to > 25 ft in open racks

Apples and oranges.

Craig L. Prahl, CET
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: [email protected] [mailto:[email protected] ] On Behalf Of Brad Casterline
Sent: Thursday, May 31, 2012 3:40 PM
To: [email protected]
Subject: RE: dry-pipe with in-rack/ceiling protection of Class IV to > 25 ft in open racks

we have an example of increasing number of heads with attic heads: 5 for wet
and 7 for dry

-----Original Message-----
From: Brad Casterline [mailto:[email protected]]
Sent: Thursday, May 31, 2012 1:26 PM
To: [email protected]; [email protected]
Subject: RE: dry-pipe with in-rack/ceiling protection of Class IV to > 25 ft
in open racks

30% more sprinkler water required due to the fire being 30% bigger due to
time delay?

-----Original Message-----
From: ParsleyConsulting [mailto:[email protected]]
Sent: Thursday, May 31, 2012 1:19 PM
To: [email protected]
Subject: Re: dry-pipe with in-rack/ceiling protection of Class IV to > 25 ft
in open racks

Scott,
    I think Scot Deal raised an interesting question.  He's correct in
the increase in area of 30%, per 12.5.1, but the question remains, if we have in-rack sprinklers, do we increase the number of them flowing in a
dry system calculation?  If so, why?  If not, why not?  The table Scot
referenced doesn't allow the use of CMDA sprinklers without in-racks as
well, so what do we do about the number flowing in the calc?

    Anyone have input on the answer?

PARSLEY CONSULTING

Ken Wagoner, SET

760.745.6181 voice

760.745.0537 fax

[email protected] <mailto:[email protected]>e-mail

www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website



On 5/31/2012 10:13 AM, Scott A Futrell wrote:
Scot,

I don't see anything that sends you back to 11.2.3.2.5 to increase the
in-rack design requirement by 30%.  11.2.3.2.5 is an area of sprinkler
operation increase, not a number of design sprinklers increase.
Intuitively, yes.  Prescriptive, no.

Scott Futrell

(763) 425-1001 x 12 Office
(612) 759-5556 Cell

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of å... ....
Sent: Thursday, May 31, 2012 11:50 AM
To: [email protected]
Subject: dry-pipe with in-rack/ceiling protection of Class IV to> 25 ft
in open racks

2010 NFPA 13

When one uses dry-pipe with combination in-rack/ceiling sprinklers to
protect Class IV to greater than 25 ft per Table 16.3.1.1, the 30% increase
applies to both in-rack and overhead sprinklers, yes?

scot deal
excelsior fire
-------------- next part --------------
An HTML attachment was scrubbed...

URL:<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120601/1810b32c/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to