Uhmmm. Yeah.... Reminds me of standing next to you and your wife in FM 
headquarters as they did their fire test and then touring their facility. This 
was one sprinkler guy that was pretty impressed with how they go about their 
business. I dare say they know a little more than most of their customers about 
fire protections so the thought of being strongarmed could be mistaken for 
education by some.

Rod at Rapid

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of George Church
Sent: Thursday, May 31, 2012 2:51 PM
To: [email protected]
Subject: RE: dry-pipe with in-rack/ceiling protection of Class IV to > 25 ft in 
open racks

But to answer your original post, Brad, YES, the 30% increase is for the 
anticipated fire growth due to the delay in water delivery.

I won't argue that an engineered solution as Scott F suggests isn't a great 
idea, but for those of us not entitled to an opinion, we look to #13 and we see 
how many sprinklers on how many levels at an end head pressure, and we flow em, 
balance to the roof with its 30% increase, and run with the minimum consensus 
prescriptive answer already there. Our building code, IBC as adopted by PA, 
doesn't require us to read into the standard and GUESS if the TC contemplated 
the situation or didn't-. That's what we do here, throwing the combined 
brainpower of ideas synergistically propelling us toward bs or the right 
answer, depending on the day,  until those who either KNOW the TC intent (and 
might have membership on Stds Council?) tell us some background, or what's in 
the works.

But for those of us with CET rather than PE or FPE, what's written in 13 is 
what we follow. If it says flow 6 sprinklers on each of two levels, that's 
twelve sprinklers, not eight and eight.

BTW, has anyone noticed a dramatic difference in the ignorance level of some of 
the Linked-In Group questions (compared to our little forum here)? I need to 
stay off them- if you've worked with FM Global, for example, would you agree 
with the guy who said he wondered how FM could get away with strong-arming 
American businesses with whatever was good for FM without a care about how much 
it cost the insured, and he hoped for the pendulum of intelligent design to 
swing the other way? Jeez, if you know anything about FM, they DO know a little 
about proper fire protection, they DO actually test things and develop valid 
criteria, I'll stop here since I'll assume I'm preaching to the choir. I'm not 
saying I agree with everything FM does, but I sure don't think their typical 
customer is strong-armed like a bunch of cowering small shopkeepers with the 
mob selling protection in their neighborhood, there are some reasonably 
intelligent people in risk management looking at the dollars invested into 
protecting their assets. Rant <OFF>


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Thursday, May 31, 2012 3:48 PM
To: [email protected]
Subject: RE: dry-pipe with in-rack/ceiling protection of Class IV to > 25 ft in 
open racks

Apples and oranges.  

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Brad Casterline
Sent: Thursday, May 31, 2012 3:40 PM
To: [email protected]
Subject: RE: dry-pipe with in-rack/ceiling protection of Class IV to > 25 ft in 
open racks

we have an example of increasing number of heads with attic heads: 5 for wet
and 7 for dry

-----Original Message-----
From: Brad Casterline [mailto:[email protected]] 
Sent: Thursday, May 31, 2012 1:26 PM
To: [email protected]; [email protected]
Subject: RE: dry-pipe with in-rack/ceiling protection of Class IV to > 25 ft
in open racks

30% more sprinkler water required due to the fire being 30% bigger due to
time delay?

-----Original Message-----
From: ParsleyConsulting [mailto:[email protected]] 
Sent: Thursday, May 31, 2012 1:19 PM
To: [email protected]
Subject: Re: dry-pipe with in-rack/ceiling protection of Class IV to > 25 ft
in open racks

Scott,
     I think Scot Deal raised an interesting question.  He's correct in 
the increase in area of 30%, per 12.5.1, but the question remains, if we 
have in-rack sprinklers, do we increase the number of them flowing in a 
dry system calculation?  If so, why?  If not, why not?  The table Scot 
referenced doesn't allow the use of CMDA sprinklers without in-racks as 
well, so what do we do about the number flowing in the calc?

     Anyone have input on the answer?

PARSLEY CONSULTING

Ken Wagoner, SET

760.745.6181 voice

760.745.0537 fax

[email protected] <mailto:[email protected]>e-mail

www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website



On 5/31/2012 10:13 AM, Scott A Futrell wrote:
> Scot,
>
> I don't see anything that sends you back to 11.2.3.2.5 to increase the
in-rack design requirement by 30%.  11.2.3.2.5 is an area of sprinkler
operation increase, not a number of design sprinklers increase.
Intuitively, yes.  Prescriptive, no.
>
> Scott Futrell
>   
> (763) 425-1001 x 12 Office
> (612) 759-5556 Cell
>
> -----Original Message-----
> From: [email protected]
[mailto:[email protected]] On Behalf Of å... ....
> Sent: Thursday, May 31, 2012 11:50 AM
> To: [email protected]
> Subject: dry-pipe with in-rack/ceiling protection of Class IV to>  25 ft
in open racks
>
> 2010 NFPA 13
>
> When one uses dry-pipe with combination in-rack/ceiling sprinklers to
protect Class IV to greater than 25 ft per Table 16.3.1.1, the 30% increase
applies to both in-rack and overhead sprinklers, yes?
>
> scot deal
> excelsior fire
> -------------- next part --------------
> An HTML attachment was scrubbed...
>
URL:<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120601/1810b32c/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________