Ohhh, couldn't the heads be 8' from each other if 8' is the min spacing?

George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Thursday, May 31, 2012 7:08 PM
To: [email protected]
Subject: Re: E/C heads: Different coverages, same area.

You can space them at anything you want up to and not less than the 
maximum/minimum spacing you're calculating for. Since minimum is 1/2 S
18x18 can't exceed 18' between heads, nor more than 9' from the wall, nor be 
closer than 9' feet to an adjacent head. just make sure the kitchen head is 
nine feet from the adjacent living room head(s) and it's an 18x18 too.

On Thu, May 31, 2012 at 3:33 PM, Ralphy Henderson <[email protected]> 
wrote:
> Is it permissable to space residential heads at two different areas of 
> coverages in the same compartment? Case: a living room making use of 18x18 
> spacing while the kitchen next to it (without a lintel or anything) is spaced 
> at 16x16. This is a 13 system (not 13R) and when calculating I'm wondering if 
> I can calc them according to this method. I know the larger demand will end 
> up driving the calculations - just want to make sure with this...
>
> Thanks,RB
> -------------- next part -------------- An HTML attachment was 
> scrubbed...
> URL: 
> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/atta
> chments/20120531/28e51b9d/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to