I think they can be different without a wall or lintel. Example 4 heads in a
square room. Heads 8' off the wall on 3 sides and 9' off on the 4th side.
Heads 16' apart. The two heads nearest the 9' off the wall are 18' x 18' and
the other two heads are 16' x 16'. I don't think this is a usual scenario but
certainly legal. Can even be more complicated if the room were 28' wide and
46' long. Heads 7' off the wall on 3 sides and 9' off on the 4th side. 16'
between the first two head in the 46' direction and 14' for the next two heads.
Now you have 18', 16', and 14' in the same room. You probably only do this due
to aesthetics and something preventing you from spacing between heads at 16'.
Simple s x l application is all that required.
Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation& Facilities Group
Burns& McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone: 952.656.3652
Fax: 952.229.2923
[email protected]
www.burnsmcd.com
Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Friday, June 01, 2012 12:43 PM
To: [email protected]
Subject: Re: E/C heads: Different coverages, same area.
I don't think so if your design basis is 18x18 and the small (I'm seeing a dog
leg off the living room for the kitchen) compartment directly communicates with
the larger no matter how small the smaller compartment is. 18x18 rules
throughout. Now if it's a separate compartment, with at least the lintel, then
that rule wouldn't necessarily apply.
On Fri, Jun 1, 2012 at 9:11 AM, George Church<[email protected]> wrote:
Ohhh, couldn't the heads be 8' from each other if 8' is the min spacing?
George L. Church, Jr., CET
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE 570-837-6335 fax
[email protected]
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron
Greenman
Sent: Thursday, May 31, 2012 7:08 PM
To: [email protected]
Subject: Re: E/C heads: Different coverages, same area.
You can space them at anything you want up to and not less than the
maximum/minimum spacing you're calculating for. Since minimum is 1/2 S
18x18 can't exceed 18' between heads, nor more than 9' from the wall, nor be
closer than 9' feet to an adjacent head. just make sure the kitchen head is
nine feet from the adjacent living room head(s) and it's an 18x18 too.
On Thu, May 31, 2012 at 3:33 PM, Ralphy Henderson<[email protected]>
wrote:
Is it permissable to space residential heads at two different areas of
coverages in the same compartment? Case: a living room making use of 18x18
spacing while the kitchen next to it (without a lintel or anything) is spaced
at 16x16. This is a 13 system (not 13R) and when calculating I'm wondering if I
can calc them according to this method. I know the larger demand will end up
driving the calculations - just want to make sure with this...
Thanks,RB
-------------- next part -------------- An HTML attachment was
scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/att
a chments/20120531/28e51b9d/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
--
Ron Greenman
Instructor
Fire Protection Engineering Technology Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405
[email protected]
http://www.bates.ctc.edu/fireprotection/
253.680.7346
253.576.9700 (cell)
Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405
[email protected]
http://www.bates.ctc.edu/fireprotection/
253.680.7346
253.576.9700 (cell)
Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum