Anytime the word storage appears there's a need for much more extensive
analysis of all of the likely materials and their configuration. For example
the 2009 International Fire Code deals with retail storage of aerosols in
Section 2806 with <8 ft and >8 ft categories.  Flammable and combustible
liquids are covered in IFC 3404.4. Then there are the Group A plastics
determined by the product itself or the packing material covered in IFC
Chapter 23.  Note the definition of high-piled high-hazard commodities could
start at >6 ft.

Ceiling height was not noted.  This could dictate maximum storage height.

Without looking at any further I'd say the chance of OH2 would be slim.

Looks like NFPA 13 is applied for the shelf storage question per IFC Section
2307.

Maybe this major chain store already has corporate guidelines.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Art Tiroly
Sent: Thursday, August 16, 2012 3:30 PM
To: [email protected]
Subject: RE: solid shelves in auto parts stores

Considering the amount of rubber and plastic parts, oil, solvents and
aerosol sprays and paint, I think it should be higher. I think in spots it
is more than a class 4 commodity. 


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Thursday, August 16, 2012 3:14 PM
To: [email protected]
Subject: solid shelves in auto parts stores

Hello,

1) There is a PE involved
2) This is not my job, but I am trying to be a friend to the AHJ'
3) I can't readily put my hands on this due to other issues


A local AHJ has called me to inquire about the requirement for protecting a
major chain Auto Parts Store. The PE has stated OH2 throughout the store.
AHJ is asking questions because there are 12' tall racks with a solid top
making him think they will store over 12'.

Questions,

Are solid shelves allowed in racks aver 30" deep in this scenario without
protection in the racks?

Is OH@ appropriate for these "typical" Auto Parts Stores with the storage as
it is?

Thanks for your help if you have time, if not please ignore and have a great
day!




--
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com> 1160
McKenzie Road Cantonment, FL 32533 850-937-1850 fax 850-937-1852
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120816/ec9499ea/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum



-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2197 / Virus Database: 2437/5203 - Release Date: 08/15/12

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to