The NAPA configuration that I had the pleasure or taking on was 24" or 30" deep 
back to back shelves up to 16'(storage on the top shelf put me up to 18' total 
height) with an intermediate open grate mezzanine (essentially two 8' storage 
racks on top of each other) and no flue space.  Aisles about 30" wide (5 or 6 
aisles) and 50 or so feet deep with a steep stair in the back corner.  
Pre-engineered rack/mezzanine structure.

Besides the obvious configuration issues, the shelving was setup so that any 
shelf could line up with the adjacent shelf giving you a 4'-5' wide by a 
minimum 8' long shelf.

Final design (PE sealed, AHJ pre-approved, Owner and Tenant Insurance companies 
in the loop) included making the tenant install treated plywood over the open 
metal grating (separating the two storage heights, placing sprinkler lines down 
each aisle at a staggared 6-7' spacing (they advised us that the top shelf of 
the lower tier may not have product on it creating a cold solder issue).  Lower 
design was to misc back-to-back shelf storage to 8', EH1 or 2 (I can't 
remember).  Overhead system was designed with the higher storage height to 12' 
all with 286 heads.  This was a strip mall (billards place and a pool store in 
the same building), luckily the suite was next to the riser room and allowed us 
to upsize only a little bit of main and all the BL.  We did remove and 
reinstall the overhead BL for the tighter spacing and tied it all back into the 
existing OH2 grid at the common wall.

A lot of extra work for such a small tenant space...


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Thursday, August 16, 2012 3:27 PM
To: [email protected]
Subject: Re: solid shelves in auto parts stores

Nobody here with experience on the AHJ or Engineering side of the following
stores:

O-reilly's
Auto Zone
Advanced Auto Parts

These are three very common retail outlets with similar arrangements.

Greg

On Thu, Aug 16, 2012 at 4:48 PM, Dale Wingard <[email protected]> wrote:

> Greg,
>
> I would take a look at Chapter 13 (10ed) for miscellaneous storage.  
> There are a lot of plastic parts for vehicles.
>
> The tables there may take you as high as EH2.
>
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Greg McGahan
> Sent: Thursday, August 16, 2012 2:14 PM
> To: [email protected]
> Subject: solid shelves in auto parts stores
>
> Hello,
>
> 1) There is a PE involved
> 2) This is not my job, but I am trying to be a friend to the AHJ'
> 3) I can't readily put my hands on this due to other issues
>
>
> A local AHJ has called me to inquire about the requirement for 
> protecting a major chain Auto Parts Store. The PE has stated OH2 throughout 
> the store.
> AHJ is asking questions because there are 12' tall racks with a solid 
> top making him think they will store over 12'.
>
> Questions,
>
> Are solid shelves allowed in racks aver 30" deep in this scenario 
> without protection in the racks?
>
> Is OH@ appropriate for these "typical" Auto Parts Stores with the 
> storage as it is?
>
> Thanks for your help if you have time, if not please ignore and have a 
> great day!
>
>
>
>
> --
> Greg McGahan
> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> fax 850-937-1852
> -------------- next part -------------- An HTML attachment was 
> scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attac
> hments/20120816/ec9499ea/attachment.html
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



--
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120816/ba3d21c5/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to