Greg,

I would take a look at Chapter 13 (10ed) for miscellaneous storage.  There are 
a lot of plastic parts for vehicles.

The tables there may take you as high as EH2.



 
-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Thursday, August 16, 2012 2:14 PM
To: [email protected]
Subject: solid shelves in auto parts stores

Hello,

1) There is a PE involved
2) This is not my job, but I am trying to be a friend to the AHJ'
3) I can't readily put my hands on this due to other issues


A local AHJ has called me to inquire about the requirement for protecting a
major chain Auto Parts Store. The PE has stated OH2 throughout the store.
AHJ is asking questions because there are 12' tall racks with a solid top
making him think they will store over 12'.

Questions,

Are solid shelves allowed in racks aver 30" deep in this scenario without
protection in the racks?

Is OH@ appropriate for these "typical" Auto Parts Stores with the storage
as it is?

Thanks for your help if you have time, if not please ignore and have a
great day!




-- 
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120816/ec9499ea/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to