You will not find anything saying the use fo underground pipe above ground is NOT ok. That's not how it works. Underground pipe by definition and allowed use per Table 10.1.1 can only be used underground (as dictated by the title of the applicable sections and listing when required). Allowed pipe material for above ground is defined by section 6.3.

There is a new allowance in the 2013 edition that will make an exception for the stub-up to the system riser to be underground pipe.

Roland

On Sep 13, 2012, at 6:58 AM, Dick Culver wrote:


I am struggling with whether it is allowable by NFPA13, 2007 edition to have approximately 100' of "underground" piping inside the building before the shutoff. In this situation, there is a meter pit outside of the building, then the UG enters the building and goes up and across to the front of the facility and connects into the fire sprinkler header. There is no valve immediately where the piping enters the building, or any means to monitor
flow.  My understanding is that this was a new UG to replace an old
dilapidated one. I have not pinpointed anything in the code that tells me
this is not ok, however it just doesn't seem to be a good practice.  I
appreciate any guidance from anyone who might have dealt with a similar
situation.



~Jarron