To extend Roland's remarks, there is also language in the new edition of
-13 (and -24) which limits the length that underground pipe can be run
under the foundation without arching, trenching or isolation valves to
no more than 10'-0" from the edge of the foundation.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[email protected] <mailto:[email protected]>e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website
On 9/13/2012 7:20 AM, Roland Huggins wrote:
You will not find anything saying the use fo underground pipe above
ground is NOT ok. That's not how it works. Underground pipe by
definition and allowed use per Table 10.1.1 can only be used
underground (as dictated by the title of the applicable sections and
listing when required). Allowed pipe material for above ground is
defined by section 6.3.
There is a new allowance in the 2013 edition that will make an
exception for the stub-up to the system riser to be underground pipe.
Roland
On Sep 13, 2012, at 6:58 AM, Dick Culver wrote:
I am struggling with whether it is allowable by NFPA13, 2007 edition
to have
approximately 100' of "underground" piping inside the building before
the
shutoff. In this situation, there is a meter pit outside of the
building,
then the UG enters the building and goes up and across to the front
of the
facility and connects into the fire sprinkler header. There is no valve
immediately where the piping enters the building, or any means to
monitor
flow. My understanding is that this was a new UG to replace an old
dilapidated one. I have not pinpointed anything in the code that
tells me
this is not ok, however it just doesn't seem to be a good practice. I
appreciate any guidance from anyone who might have dealt with a similar
situation.
~Jarron
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120913/71ab1b7a/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum