>From the 2009 IFC Commentary;

905.3.4 Stages

"Because of the potentially large fuel load and three-dimensional aspect of
the fire hazard associated with stages greater than 1,000 square feet (93
m2) in area, Class III standpipes are required on each side of these large
stages. The standpipes must be equipped with a 1-inch (25 mm) and a 2-inch
(51 mm) hose connection. The 1-inch (25 mm) connection is for the hose
requirement in Section 905.3.4.1. The 21/2-inch (64 mm) connection is to
provide greater flexibility for the fire department in its fire-fighting
operations.

Stages, as used in this section, are those that are defined in Section 410.2
of the IBC, which include overhead hanging curtains, drops, scenery or stage
effects other than lighting and sound. These were traditionally referred to
as “legitimate stages.” It is not an appropriate application of this section
to require standpipes for elevated areas in banquet rooms or theatrical
platforms where the higher fuel loads associated with a legitimate stage do
not exist.

The exception recognizes the benefit of the building or area being
sprinklered. If so, then only the 11/2-inch (38 mm) connection is required.
This hose connection is intended to be used by the fire department so to
apply less water from the hose due to the suppression activity of the
sprinkler system. Hose threads must be compatible with those of the fire
department as required in Section 903.3.6. In a fully sprinklered building
it is acceptable to supply the hose connections through the same standpipe
as the sprinklers. This is reflected in the reference to both NFPA 13, which
acknowledges this concept and NFPA 14, which contains similar provisions. If
the provisions of NFPA 14 are used, although the standpipe must be wet and
Class II in its installation, the design of the water supply and
interconnection of systems can be in accordance with the requirements for
Class II as well as for Class III standpipes."

Hope that helps,

John Drucker, CET
Fire Protection Subcode Official
Fire / Building / Electrical Inspector
New Jersey



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve
Leyton
Sent: Thursday, October 10, 2013 1:16 PM
To: [email protected]
Subject: RE: Stages

Because a curtain drawn horizontally across the front of a platform that
doesn't have the fly space over it doesn't represent the same hazard as a
truly elevated "hanging curtain".   With a platform condition, the ceiling
is generally continuous from the seating area to the over-platform area.
You have sprinklers on both sides of a drawn curtain without the various
influences of a fly space such as obstructions, very high clearance to
sprinklers, etc.

Steve L




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Cahill,
Christopher
Sent: Thursday, October 10, 2013 10:13 AM
To: [email protected]
Subject: RE: Stages

How is the curtain you reference in a school not a "overhead hanging
curtains"?  Just asking as it seems the plain language they are curtains
that hang from above one's head level.  That said I'm not sure the
interpretation is that far out of whack.  I always thought (because perhaps
I made it up to justify in my own mind) the curtain issue was related to the
audience cut off from the going's on behind the curtain and the potential
for delay in recognizing a developing threat.  Granted any other wall in the
building does that.  But most walls are of hard construction that don't add
to the fire load and last a lot longer than a curtain. 

I agree a legit stage has higher hazards and in the definition is covered
with drops, scenery or stage effects.  And all platforms I have seen with a
curtain are used more like a stage, at least occasionally, than those
without a curtain with regards to fire hazards.  But maybe I need to get out
more. 

Chris Cahill, PE*
Senior Fire Protection Engineer
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in:
MN





-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve
Leyton
Sent: Thursday, October 10, 2013 11:58 AM
To: [email protected]
Subject: RE: Stages

At 1600 sq. ft. a stage also requires a Class III standpipe, with an
exception for fully sprinklered buildings that allows the installation of a
small hose connection.

We have wrestled with this here in CA because our state AHJ for schools has
formally interpreted the IBC definition that speaks to "overhead hanging
curtains" to include any curtain that hangs from its hardware, including the
usual one at the stage front that closes horizontally.
So in school assembly areas, multi-purpose buildings and gyms that have a
platform by definition, it's a stage if there's a curtain that closes
it off from the A-occupancy area.   I fundamentally disagree with this
interp, but that's how we play it out here in that jurisdiction.

The intent of the proscenium separation and higher level of sprinkler
protection (OH) in the fly space over a legitimate stage has to do with the
aerial suspension of fire load.  Cardboard, wood and fabric set pieces,
tapestries, painted panels of all types and various other things that can be
hung from the rigging are all, generally, HIGHLY flammable.
Elevating the fire load enhances airflow and leads to falling/flying
brands.   We had a fire at the Civic Theater in San Diego a few years
back and it operated four sprinklers over the fly space (75' AFF, I think).


All this underscores that legitimate stages and platforms are actually very
different animals, but also that AHJ's will do what they do ...

Steve L




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Craig
Leadbetter
Sent: Thursday, October 10, 2013 7:43 AM
To: [email protected]
Subject: RE: Stages

Well unfortunately the drawing does say stage and the area is approx.
1600 sqft. 



Craig Leadbetter

Safeguard of Marquette
PO Box 116
Marquette, MI 49855


(P) 906-475-9955
(F) 906-475-5474
(C) 906-362-5393



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
rongreenman .
Sent: Thursday, October 10, 2013 10:35 AM
To: [email protected]
Subject: Re: Stages

According to an AHJ I had to deal with once, it was a stage if the architect
wrote stage and a platform if he wrote platform. This opened up so many
possibilities.


On Thu, Oct 10, 2013 at 6:59 AM, Cahill, Christopher
<[email protected]>wrote:

> It's defined twice in IBC
>
> Inversely in the definition for PLATFORM. A raised area within a 
> building used for worship, the presentation of music, plays or other 
> entertainment; the head table for special guests; the raised area for 
> lecturers and speakers; boxing and wrestling rings; theater-in-the 
> round stages; and similar purposes wherein there are no overhead 
> hanging curtains, drops, scenery or stage effects other than lighting 
> and
sound.
>
> And STAGE. A space within a building utilized for entertainment or 
> presentations, which includes overhead hanging curtains, drops, 
> scenery or stage effects other than lighting and sound.
>
> So do you have curtains, drops, scenery or other stage effects?  Note 
> size does not matter, storage underneath does not matter when defining

> whether you have a stage or not.
>
> Chris Cahill, PE*
> Senior Fire Protection Engineer
> Burns & McDonnell
> 8201 Norman Center Drive
> Bloomington, MN 55437
> Phone:  952.656.3652
> Fax:  952.229.2923
> [email protected]
> www.burnsmcd.com
>
> Proud to be one of FORTUNE's 100 Best Companies to Work For 
> *Registered in: MN
>
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of 
> [email protected]
> Sent: Thursday, October 10, 2013 8:40 AM
> To: [email protected]
> Subject: RE: Stages
>
> IFC 905.3.4 ('06 ed) kicks in the hose valve requirement at greater 
> than
> 1000 sqft. So I guess a "stage" can be under 1000 sqft. but the hose 
> valves wouldn't be required.
>
> Ron F
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Richard 
> Lindner
> Sent: Thursday, October 10, 2013 4:46 AM
> To: sprinklerforum@lists firesprinkler. org
> Subject: Re: Stages
>
> You need to use the appropriate building code to determine platform vs

> stage for this area of the country. If stage, square footage and 
> ability to store under will also come into play.
>
> Richard
> On Oct 10, 2013 7:06 AM, "Craig Leadbetter" 
> <[email protected]>
> wrote:
>
> >
> >
> > At what point does a stage become a stage rather than just a raised 
> > platform?
> >
> > I am working on a project that is an old school that is being 
> > converted to apartments, however a portion of the building will 
> > remain as an educational classification with a school "stage" in the

> > gymnasium portion of the building.
> >
> > Should I be looking at this as a full blown "stage" and all of the 
> > hose stations and such or am I over thinking? I am trying to 
> > eliminate the need for a fire pump.
> >
> > No, I can't ask the engineer. we basically got an x through the 
> > drawings and says provide fire protection to meet code.
> >
> > Thanks
> >
> >
> > Craig Leadbetter
> >
> > Safeguard of Marquette
> > PO Box 116
> > Marquette, MI 49855
> >
> >
> > (P) 906-475-9955
> > (F) 906-475-5474
> > (C) 906-362-5393
> >
> >
> >
> >
> >
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > kl
> > er.org
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to