Because a curtain drawn horizontally across the front of a platform that 
doesn't have the fly space over it doesn't represent the same hazard as a truly 
elevated "hanging curtain".   With a platform condition, the ceiling is 
generally continuous from the seating area to the over-platform area.   You 
have sprinklers on both sides of a drawn curtain without the various influences 
of a fly space such as obstructions, very high clearance to sprinklers, etc.

Steve L




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Cahill, 
Christopher
Sent: Thursday, October 10, 2013 10:13 AM
To: [email protected]
Subject: RE: Stages

How is the curtain you reference in a school not a "overhead hanging curtains"? 
 Just asking as it seems the plain language they are curtains that hang from 
above one's head level.  That said I'm not sure the interpretation is that far 
out of whack.  I always thought (because perhaps I made it up to justify in my 
own mind) the curtain issue was related to the audience cut off from the 
going's on behind the curtain and the potential for delay in recognizing a 
developing threat.  Granted any other wall in the building does that.  But most 
walls are of hard construction that don't add to the fire load and last a lot 
longer than a curtain. 

I agree a legit stage has higher hazards and in the definition is covered with 
drops, scenery or stage effects.  And all platforms I have seen with a curtain 
are used more like a stage, at least occasionally, than those without a curtain 
with regards to fire hazards.  But maybe I need to get out more. 

Chris Cahill, PE*
Senior Fire Protection Engineer
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in: MN





-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve 
Leyton
Sent: Thursday, October 10, 2013 11:58 AM
To: [email protected]
Subject: RE: Stages

At 1600 sq. ft. a stage also requires a Class III standpipe, with an exception 
for fully sprinklered buildings that allows the installation of a small hose 
connection.

We have wrestled with this here in CA because our state AHJ for schools has 
formally interpreted the IBC definition that speaks to "overhead hanging 
curtains" to include any curtain that hangs from its hardware, including the 
usual one at the stage front that closes horizontally.
So in school assembly areas, multi-purpose buildings and gyms that have a 
platform by definition, it's a stage if there's a curtain that closes
it off from the A-occupancy area.   I fundamentally disagree with this
interp, but that's how we play it out here in that jurisdiction.

The intent of the proscenium separation and higher level of sprinkler 
protection (OH) in the fly space over a legitimate stage has to do with the 
aerial suspension of fire load.  Cardboard, wood and fabric set pieces, 
tapestries, painted panels of all types and various other things that can be 
hung from the rigging are all, generally, HIGHLY flammable.
Elevating the fire load enhances airflow and leads to falling/flying
brands.   We had a fire at the Civic Theater in San Diego a few years
back and it operated four sprinklers over the fly space (75' AFF, I think).  

All this underscores that legitimate stages and platforms are actually very 
different animals, but also that AHJ's will do what they do ...

Steve L




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Craig 
Leadbetter
Sent: Thursday, October 10, 2013 7:43 AM
To: [email protected]
Subject: RE: Stages

Well unfortunately the drawing does say stage and the area is approx.
1600 sqft. 



Craig Leadbetter

Safeguard of Marquette
PO Box 116
Marquette, MI 49855


(P) 906-475-9955
(F) 906-475-5474
(C) 906-362-5393



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of 
rongreenman .
Sent: Thursday, October 10, 2013 10:35 AM
To: [email protected]
Subject: Re: Stages

According to an AHJ I had to deal with once, it was a stage if the architect 
wrote stage and a platform if he wrote platform. This opened up so many 
possibilities.


On Thu, Oct 10, 2013 at 6:59 AM, Cahill, Christopher
<[email protected]>wrote:

> It's defined twice in IBC
>
> Inversely in the definition for PLATFORM. A raised area within a 
> building used for worship, the presentation of music, plays or other 
> entertainment; the head table for special guests; the raised area for 
> lecturers and speakers; boxing and wrestling rings; theater-in-the 
> round stages; and similar purposes wherein there are no overhead 
> hanging curtains, drops, scenery or stage effects other than lighting 
> and
sound.
>
> And STAGE. A space within a building utilized for entertainment or 
> presentations, which includes overhead hanging curtains, drops, 
> scenery or stage effects other than lighting and sound.
>
> So do you have curtains, drops, scenery or other stage effects?  Note 
> size does not matter, storage underneath does not matter when defining

> whether you have a stage or not.
>
> Chris Cahill, PE*
> Senior Fire Protection Engineer
> Burns & McDonnell
> 8201 Norman Center Drive
> Bloomington, MN 55437
> Phone:  952.656.3652
> Fax:  952.229.2923
> [email protected]
> www.burnsmcd.com
>
> Proud to be one of FORTUNE's 100 Best Companies to Work For 
> *Registered in: MN
>
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of 
> [email protected]
> Sent: Thursday, October 10, 2013 8:40 AM
> To: [email protected]
> Subject: RE: Stages
>
> IFC 905.3.4 ('06 ed) kicks in the hose valve requirement at greater 
> than
> 1000 sqft. So I guess a "stage" can be under 1000 sqft. but the hose 
> valves wouldn't be required.
>
> Ron F
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Richard 
> Lindner
> Sent: Thursday, October 10, 2013 4:46 AM
> To: sprinklerforum@lists firesprinkler. org
> Subject: Re: Stages
>
> You need to use the appropriate building code to determine platform vs

> stage for this area of the country. If stage, square footage and 
> ability to store under will also come into play.
>
> Richard
> On Oct 10, 2013 7:06 AM, "Craig Leadbetter" 
> <[email protected]>
> wrote:
>
> >
> >
> > At what point does a stage become a stage rather than just a raised 
> > platform?
> >
> > I am working on a project that is an old school that is being 
> > converted to apartments, however a portion of the building will 
> > remain as an educational classification with a school "stage" in the

> > gymnasium portion of the building.
> >
> > Should I be looking at this as a full blown "stage" and all of the 
> > hose stations and such or am I over thinking? I am trying to 
> > eliminate the need for a fire pump.
> >
> > No, I can't ask the engineer. we basically got an x through the 
> > drawings and says provide fire protection to meet code.
> >
> > Thanks
> >
> >
> > Craig Leadbetter
> >
> > Safeguard of Marquette
> > PO Box 116
> > Marquette, MI 49855
> >
> >
> > (P) 906-475-9955
> > (F) 906-475-5474
> > (C) 906-362-5393
> >
> >
> >
> >
> >
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > kl
> > er.org
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________