Steve, I once ran a scenario where ten 36" ducts ran parallel, 18" below the ceiling deflectors, with a 1" gap between each. Make the ducts 47" if you like and the gaps 3" if you like. Meets the rule but you essentially would have 30-50 feet of solid with waterfalls every three or four feet. I can't remember whether it was Phil or Roland that wrote the informal response to my question, whomever agreed that it met the standard. Fixing this little loophole?
On Tue, Jan 7, 2014 at 1:19 PM, Steven Scandaliato <[email protected]>wrote: > Today...it is whatever you and the AHJ agree on. Hopefully (fingers > crossed) we will have a clear definition in the next edition as we are > working at adding the "gaps and clouds" section and with this will come new > definitions including concealed spaces and the 4ft rule. Hold your breath! > Haha. > > Steven Scandaliato, SET CFPS > 520.971.2322 Cell > Skype: steven.scandaliato > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Todd > - > Work > Sent: Tuesday, January 07, 2014 3:12 PM > To: [email protected] > Subject: concealed space definition > > Is there an official definition of a concealed space? Is a 10 ft x 20 ft > platform that is 9" off the ground but not enclosed on the sides considered > a concealed space? > > Todd G Williams, PE > Fire Protection Design/Consulting > Stonington, CT > www.fpdc.com > 860-535-2080 (ofc) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) A problem well stated is a problem half solved. -Charles F. Kettering, inventor and engineer (1876-1958) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org