What does the structural design notes sheet provide? Is it Seismic Category C or higher. If so, bracing is required on fire sprinkler systems. I don't think the seismic maps really apply any longer. You need to know the Seismic Design Category, then you need the Ss values so you can calculate your bracing.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

On 1/23/2014 9:15 AM, Richard Mote wrote:
Can someone with experience in the area tell me if Seismic bracing is required 
in Fredrick Maryland? (21701) According to the maps I found online at appears 
to be the same seismic category as central PA, but not having worked in the 
area before I wanted to be sure there wasn't some local requirement.

Richard L. Mote
Rowe Sprinkler Systems, Inc.
7994 Route 522, Suite 1
PO Box 407
Middleburg, PA 17842
P 570-837-7647
F 570-837-6335