We had a few in offsite structures that were removed right before I started because there wasn't any industry standard practice documentation to support them, several buildings started having a lot of false trip issues afterward though. Ultimately we elected to install air vents which seem to have mostly cured the issues. Our main campuses are supplied by large fire pump arrangements that keep the pressures pretty consistent (and high) but off site buildings that didn't need a pump still had one in the type of arrangement you've noted.
Mike Morey, CFPS, SET Planner Scheduler/Designer BMWC Constructors, Inc. 1740 W. Michigan St, Indianapolis, IN 46222 O: 317.651.0596 | C: 317.586.8111 [email protected] | www.bmwc.com ________________________________________ From: [email protected] [[email protected]] on behalf of Matt Grise [[email protected]] Sent: Friday, January 31, 2014 11:56 AM To: [email protected] Subject: jockey pump only I ran across a system where the owner has elected to use a small pump to pressurize the system in order to prevent municipal water surges from causing false trips on the flow switch. Has anyone seen this before? Are there any codes that address something like this? (not something that we installed, or specified... just found it this way) Matt Grisé PE*, LEED AP, NICET II Sales Engineer Alliance Fire Protection 130 w 9th Ave. North Kansas City, MO 64116 *Licensed in KS & MO 913.888.0647 ph 913.888.0618 f 913.927.0222 cell www. AFPsprink.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org