In New Zealand most of our Fire Sprinkler Systems have this arrangement of a
manually controlled super-pressure pump which is used to raise the
installation pressure above the sprinkler alarm valve by approx 450 kPa.
This allows us to have two pressure sensor settings at approx 150 kPa
intervals for signalling defect and fire. If the water supply pressure is
say 500kPa then the installation standing pressure would be 950kPa. Defect
would be signalled at 800 kPa and Fire at 650 kPa. Most of our systems are
connected to a national receiving centre. Defect calls are on sent to
maintenance company and fire calls go direct to the Fire Service. This is
specified in our New Zealand Standard NZS 4541. We still have a water motor
alarm gong on the building.

Russell Gregory
Special Projects Engineer 
Wormald
Christchurch, NZ

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Matt
Grise
Sent: Saturday, 1 February 2014 5:57 a.m.
To: [email protected]
Subject: jockey pump only

I ran across a system where the owner has elected to use a small pump to
pressurize the system in order to prevent municipal water surges from
causing false trips on the flow switch. Has anyone seen this before? Are
there any codes that address something like this?

(not something that we installed, or specified... just found it this way)

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to