Same in Australia, but far less sophisticated.
Use a small Jacking pump to raise the system pressure just above the likely
peak towns main pressure for sprinkler systems.
We use the term jockey pump to maintain a high pressure on a combined
sprinkler  / hydrant pump system on a larger "site wide"  fire  mains
system.
Hope this helps.

Carl Rickard
AFPR.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Russell
& Carol Gregory
Sent: Saturday, 1 February 2014 6:30 PM
To: [email protected]
Subject: RE: jockey pump only

In New Zealand most of our Fire Sprinkler Systems have this arrangement of a
manually controlled super-pressure pump which is used to raise the
installation pressure above the sprinkler alarm valve by approx 450 kPa.
This allows us to have two pressure sensor settings at approx 150 kPa
intervals for signalling defect and fire. If the water supply pressure is
say 500kPa then the installation standing pressure would be 950kPa. Defect
would be signalled at 800 kPa and Fire at 650 kPa. Most of our systems are
connected to a national receiving centre. Defect calls are on sent to
maintenance company and fire calls go direct to the Fire Service. This is
specified in our New Zealand Standard NZS 4541. We still have a water motor
alarm gong on the building.

Russell Gregory
Special Projects Engineer
Wormald
Christchurch, NZ

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Matt
Grise
Sent: Saturday, 1 February 2014 5:57 a.m.
To: [email protected]
Subject: jockey pump only

I ran across a system where the owner has elected to use a small pump to
pressurize the system in order to prevent municipal water surges from
causing false trips on the flow switch. Has anyone seen this before? Are
there any codes that address something like this?

(not something that we installed, or specified... just found it this way)

Matt Grisé PE*, LEED AP, NICET II
Sales Engineer
Alliance Fire Protection
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 

913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2013.0.3462 / Virus Database: 3684/7050 - Release Date: 01/31/14


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to