"Hello Matt,

ADT used to have one called a 6121. It had 3 stages to the pressure switch. 1st 
would only run the pump, 2nd would send a trouble signal if the pressure kept 
falling, 3rd was the waterflow signal. Used to set them about 40 PSI over the 
static.

We still have a Hydro pump with the same head on it in use.

Friday, January 31, 2014, 11:56:49 AM, you wrote:

> I ran across a system where the owner has elected to use a small
> pump to pressurize the system in order to prevent municipal water
> surges from causing false trips on the flow switch. Has anyone seen
> this before? Are there any codes that address something like this?

> (not something that we installed, or specified... just found it this way)