What's the jockey set at?  Isn't it typically higher?  FWIW I'd flag you for 
the 3 psi too.  They have no choice liability wise.  If something ever breaks 
they (I) don't want the liability. 

But I also understand it's only 7' up and the issue is resolved.  As long as 
everything from the pump discharge to 7' above is high pressure listed I'd then 
be OK with it.  Another issue is it's +3 today but what is the peak static 
pressure.  Could be even higher in the future with normal sloshing of water in 
the city system. 

Chris Cahill, PE*
Associate Fire Protection Engineer 
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, February 18, 2014 1:50 PM
To: [email protected]
Subject: Static Pressure/Working Pressure

3.8.1.9.2 Static Pressure. The pressure that exists at a given point under 
normal distribution system conditions measured ...
We have a project with an electric pump and when combined with the current 
water supply the churn pressure is 178 psi. A nationally known engineering firm 
wants us to install PRV's on the lowest level of the building because of the 3 
psi. Our position is that the pressure only exists at churn and that is similar 
to an overnight pressure surge in a municipal water system. The over pressure 
will be compensated for by the pressure relief valves once the pump stops. Are 
we being overly loose with our interpretation of "normal" or is the engineering 
firm correct?
Ron F  

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to